    Oil changeover from mineral oil to POE in compressor



    Hello,

    We have a reciprocating semi hermetic compressor with mineral oil and i want to change oil to POE because i want to use this compressor in a cooling unit running with R407C...

    First of all i would like to learn how can i removed the mineral oil from the compressor and before add the POE lubricant i have to vacuum the compressor or not? If these lubricants are mixed each other a little, is there any problem in running the system?

    I hope i explain my questions enough...


    Best Regards



  2. #2
    Join Date
    Oct 2001
    Location
    Scotland
    Age
    67
    Posts
    20
    Rep Power
    0
    To change over to POE you need to:
    1 Drain the mineral oil & fill the comp with POE.
    2 Run the system with with the existing refrigerant using POE
    3 After several hours of running test the oil with a suitable test kit that is available from most outlets or refrigerant suppliers.
    4 Keep changing the oil until the test shows that the mineral oil content is down to the required amount (normally <1%).
    5 Recover the existing refrigerant.
    6 Change any driers & components not suitable for the new refrigerant I.E. Xvalve elements, gaskets, O rings & seals (most should be OK but its worth checking).
    7 Pressure test with OFN.
    8 Evacuate the system to a good vacuum. 4 mbar should suffice except in low ambients, but thats a whole other subject.
    9 Recharge with the new refrigerant & recommission the plant.
    Remember to adjust pressure switch settings to suit the new gas.
    & clearly mark the plant to show what gas it is now running on.

    PS where in Turkey are you working? I spent some time working in Istanbul.
    Last edited by david.findlay; 07-03-2003 at 07:52 PM.

  3. #3
    Join Date
    Jan 2002
    Location
    turkey
    Age
    54
    Posts
    22
    Rep Power
    0
    Thanks for your answer Mr.Findlay,

    I am working in Alarko , İstanbul... I don't know Do you know Alarko before, but we produced ahu, cooling units, fancoil and other products related with heating in our factory.

    Could you please tell me i have any chance to understand the quantity of left mineral oil without runing the system?

    Your answer wil be appreciated...

    Regards

    Aygul

  4. #4
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi aygul,
    If your are fitting a secondhand compressor that has run on mineral oil onto a system that has been running on poly oil, simply change the compressor oil. Run the system up as you would after fitting any compressor (including a pressure test and evacuation), then test the oil after running for a few hours, that will allow you to detemine when you need to change the oil and when to re-test the oil.
    If the compressor is dry inside, and it should if you are considering fitting it to a refrigeration system, you do not need to vac it out before adding oil.
    Poly oil will not react with mineral oil in the short term, but over a period of month, under extreme load conditions. If you test and change the oil during the inital commissioning stages and you have a clean system to start with, poly oil will not cause ant adverse affects to your system in the long term
    Regards. Andy.

  5. #5
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    There is one consideration that nobody has mentioned yet. The POE oil is an effective solvent. If you have carbonization deposits anywhere in the system, they will be loosened and clog small orifices such as TEV valves, filter screens, Sentronic oil failure sensors, etc.

    Be prepared to clean these within days of changing the oil even if you have put new filters in.

  6. #6
    mike hamel's Avatar
    mike hamel Guest

    poe oil

    Dan is right-- POE oil is a great solvent. When we convert from R12 (mineral oil) to R134a (POE oil), we get a crud-burst that lasts for days.

    We put felt socks in strainers, and open-inspect them every few days.

    We also have to change dehydrator cartridges very frequently for several months. They get clogged up.

  7. #7
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    we get a crud-burst that lasts for days.
    I love it! Can I use that phrase without copyright infringement?

Similar Threads

  1. can overfilling/overcharging damage a compressor?
    By fredjchavez in forum Trouble Shooting
    Replies: 10
    Last Post: 12-02-2009, 10:30 AM
  2. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 10:50 PM
  3. One Half of a Part Wound Compressor Motor is Burnt
    By aygul in forum Trouble Shooting
    Replies: 2
    Last Post: 25-08-2003, 11:11 AM
  4. Compressor failure...... cause
    By herefishy in forum Technical Speculations
    Replies: 8
    Last Post: 06-12-2002, 12:15 AM
  5. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •