    Smile Lennox KNHK 43E



    Hi All

    Attended site to complaints of Lennox air cooled unit tripping out.
    Checked over found motor protection device stopping compressor.
    Bypassed MPD for a short period of time to find the low/high side refrigerant pressures doing hardly nothing.
    Also found paint on compressor head to be badly cracked.
    Could anyone help me with this problem.



  2. #2
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Lennox KNHK 43E

    Sounds like the compressor is not starting up properly.

    Check the capacitors and starting relay.

    Then repaint the comp.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  3. #3
    Join Date
    Nov 2007
    Location
    Peoples Republic of Geordie Land
    Posts
    47
    Rep Power
    0

    Re: Lennox KNHK 43E

    Chillin Out

    The compressor is 3 phase.

    No cappys and relays on this one.

    CoolKids

  4. #4
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: Lennox KNHK 43E

    CoolKids
    I presume this is a semi and from the info it sounds like the compressor has been getting pretty hot.
    If there is little difference between suction and discharge I would say the valves are shot and therefore not pumping and very little cold gas coming back to cool the windings causing the thermistor relay to trip.
    Pull the compressor out and replace with a new or rebuilt one.
    Paul

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Thumbs up Re: Lennox KNHK 43E

    CoolKids
    PaulZ is absolutely correct.
    On any recip if there is little or no difference between the suction and discharge pressures.
    Then it's a safe bet that the compressor is not compressing the refrigerant vapour. And the first thing to suspect is the valves being worn and no longer being gas tight. Also as a consequence of passing discharge valves. High head temperatures can be experianced (badly cracked paint on the head!)
    Also as Paul mentioned, semi hermetic compressors rely on the cooling effect of the suction gases. Flowing through the windings to
    cool the motor.
    Dependant on wether you or your collegues strip and rebuild these comps?
    Will determine your next move.
    Grizzly

  6. #6
    Join Date
    Nov 2007
    Location
    Peoples Republic of Geordie Land
    Posts
    47
    Rep Power
    0

    Re: Lennox KNHK 43E

    Grizzly& PaulZ
    Thanks for your help.

    Cheers

    CoolKids

Similar Threads

  1. lennox heat pump kfhk 28 vfc
    By cool it in forum Air Conditioning
    Replies: 11
    Last Post: 23-02-2007, 07:34 PM
  2. Lennox Heat Pumps !
    By cool it in forum Air Conditioning
    Replies: 4
    Last Post: 21-12-2006, 09:39 PM
  3. Lennox fan coil unit question
    By THERMOACC in forum Fundamentals
    Replies: 2
    Last Post: 17-02-2006, 10:31 PM
  4. Lennox outdoor unit
    By frankmcbride in forum Air Conditioning
    Replies: 7
    Last Post: 16-03-2004, 07:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •