Thread: Eliwell
26-11-2007, 05:59 PM #1
Eliwell
I got some very good advice from this site earlier and thought i had sorted the problem out but now a fault code [ AH1 ] has appeared on the contoller. Does anyone know what this fault code is and how to solve. The system has an Eliwell ID 974 controller.
Any help will be greatfull
Wazzer
26-11-2007, 07:18 PM #2
Re: Eliwell
Hi Wazzer
Its the high temp allarm, probe 1 (thermostat probe)
Hope this helps
Pete
26-11-2007, 08:52 PM #3
Re: Eliwell
Hope this might help.
Sorry, noticed that it is in dutch.Last edited by on4hf; 26-11-2007 at 08:56 PM.
14-12-2007, 01:40 AM #4
Re: Eliwell
wazzer.
Go to my link ALARM CODES in refrigeration Books
and follow the link.
scroll down page to alarm code Tech. Bulletin. Open it and select ID974 pdf.
14-12-2007, 05:10 PM #5
Re: Eliwell
Wazzer
High temperature alarm (referred tothe thermostat probe or probe 1)
it is on page 2 of 6 of the Manual.
19-12-2007, 09:11 AM #6
Re: Eliwell
You should find HAL and change it to higher value. Of course, you should do that if everything else is fine.
HAL means High temp. alarm. An example: if your Set Point value is +2C and HAL is 10 then you should get AH when temp. reach 12C. If you change HAL to 15 then AH will show up when temp reach 17C.
First of all you should find a reason for high temp.
Eliwell IWC 730
By klimek in forum ElectricalReplies: 3Last Post: 11-09-2007, 11:53 AM -
Eliwell ID974
By GVLax50 in forum ElectricalReplies: 15Last Post: 07-09-2007, 04:56 PM -
Eliwell amp controller EV782
By alan thompson in forum CommercialReplies: 1Last Post: 28-02-2007, 06:06 PM -
Eliwell Ewpc 961
By KCDOMAPPS in forum CommercialReplies: 6Last Post: 26-02-2007, 06:57 PM -
Eliwell ECH 210
By chemi-cool in forum Trouble ShootingReplies: 6Last Post: 03-09-2006, 12:51 PM