View Poll Results: Am i right?
- Voters
- 58. You may not vote on this poll
-
Yes, you are correct. high side pressure on start up does not exceed the normal working high side pressure.
48 82.76% -
No, your friend is correct. high side pressure does skyrocket on the startup. (please post why, i would really like to know)
10 17.24%
Results 1 to 38 of 38
Thread: please settle this debate
Hybrid View
-
13-11-2007, 12:52 PM #1
Re: please settle this debate
This is pretty much it, when a unit starts it's going to be at it's highest suction pressure, which means the head pressure will be highest.
I was working on a upright freezer yesterday. Ambient was 39C, but it was hotter than that due to all the other condensing units.
After defrosting the coil (so the evap coil was warm), I couldn't get the damn thing running again. It kept on tripping out for some reason, while all the other freezers at -18 were cycling fine.
So I had to increase HP cut out from 2600Kpa to 2800kpa just to get it started.
edit: Nothing changed on the system, it was cycling fine, not tripping out the 2600kPa HP before I defrosted it.Last edited by paul_h; 13-11-2007 at 12:54 PM.
Similar Threads
-
Superheat debate
By zolar1 in forum Technical DiscussionsReplies: 5Last Post: 08-02-2008, 09:57 PM