    SY Cable



    Hi

    We've recently found that SY cable is not allowed for outdoor use due to it not being UV rated, if you look at older installations you can see the effect.

    What other alternatives are there to SWA as SWA is a nightmare to terminate with ac units. The only way to earth the armour with smaller splits is to link an earth cable from the interconnecting isolator gland. This needs to be 4mm if it comes from outside of the isolator.

    I reckon 80% of installations use SY.

    Any ideas?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: SY Cable

    How about FP200 in white?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: SY Cable

    This is what I have been using the last six months, probably quicker to install than SY, alot tougher and looks better with your pipework. The solid core makes crimping easier too. Give it a go for the same price as SY you cant go wrong.

    http://www.actionlampco.com/evertuf.htm

    Cheers

  4. #4
    Celcius's Avatar
    Celcius Guest

    Re: SY Cable

    I thought most manufacturers advise against solid cores.

    Do you put a crimp on to terminate?

    I also thought crimps were only for use on stranded core cable.

  5. #5
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: SY Cable

    I use the red ring crimps on all terminals, you have to use these for the earth at least on most splits as the earth connection is on a seperate plate sometimes.

  6. #6
    Join Date
    Nov 2007
    Location
    England
    Age
    48
    Posts
    2
    Rep Power
    0

    Re: SY Cable

    I use Evertuff as well, it is good.

  7. #7
    Join Date
    Nov 2006
    Location
    Cheshire, UK
    Age
    56
    Posts
    360
    Rep Power
    18

    Re: SY Cable

    Being an Electrician as my 'first' trade can you quote me a Reg No' from BS7671 that forbids SY for use outdoors?

  8. #8
    Join Date
    Aug 2005
    Location
    uk
    Age
    46
    Posts
    82
    Rep Power
    19

    Re: SY Cable

    i'd be interested to to know the outcome of this, as we currently use sy

  9. #9
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: SY Cable

    Just googled SY cable and found this:

    http://www.voltimum.co.uk/consult.ph...onsult&id=4737

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: SY Cable

    Quote Originally Posted by Celcius View Post
    What other alternatives are there to SWA as SWA is a nightmare to terminate with ac units. The only way to earth the armour with smaller splits is to link an earth cable from the interconnecting isolator gland. This needs to be 4mm if it comes from outside of the isolator.
    Don't forget that the steel braiding on SY should also be earthed. There are special terminals available for this.

    Why does the seperate earth from the isolator gland need to be 4mm? Surely it should be sized in accordance with BS7671 and be dependant upon the size of the phase cores, i.e. you wouldn't use 4mm earth if the supply was in 6mm or 10mm

  11. #11
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: SY Cable

    I heard this SY is banned thing about 12 months ago. Turned out it was one of the big M&E contractors who disallowed it on their jobs. I think it was AMEC, or Matthew Hall as they are called once again.

    I personally use SY with the correct glands, and have never suffered this "UV unstable" rubbish. What i have seen is rusty waterlogged braiding due to cheap stuffin glands having been used.

    Cheers

    eggs

  12. #12
    Join Date
    Mar 2007
    Location
    england
    Age
    45
    Posts
    78
    Rep Power
    18

    Re: SY Cable

    Our company also uses evertuff and have not had any problems. I think it makes an install tidy as it is black and we also use black condensate drain.

  13. #13
    Celcius's Avatar
    Celcius Guest

    Re: SY Cable

    Apparantly 4mm cable is the minimum size when running earths as a singular.

    It was a BT site where the chillers were wired in SY. The cable had to be stripped out after a couple of years, although apparantly the roof is a bit of a sun trap.

    Also a consultant snagged some SY cable on a another site. Not sure of the outcome of that one though.

  14. #14
    Join Date
    Mar 2005
    Location
    North Yorks
    Posts
    10
    Rep Power
    0

    Re: SY Cable

    Quote Originally Posted by ram View Post
    I use Evertuff as well, it is good.
    Evertuff sounds good, please can someone post some details on it web site/supplier

    Thanks

Similar Threads

  1. cable current carrying capacity
    By nickruf in forum Electrical
    Replies: 6
    Last Post: 23-05-2007, 04:22 PM
  2. Running out of cable...
    By nh3simman in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 08-04-2007, 04:22 PM
  3. Wire Capacities
    By Latte in forum Electrical
    Replies: 20
    Last Post: 21-10-2006, 06:44 PM
  4. Cable current carrying capacity
    By Abe in forum Electrical
    Replies: 72
    Last Post: 25-09-2005, 10:23 PM
  5. Armoured cable
    By bernard in forum Electrical
    Replies: 7
    Last Post: 02-04-2005, 06:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •