    Question discharge pressure too high



    hello everybody...

    i'm new in refrigeration so i want to know why the discharge pressure is to high even if i run only 1 compressor.the pressure is 50 psi suction & 225 psi discharge,if i run 2 compressor,suction pressure is the same value but discharge will go higher to 300 psi.can you help me...



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: discharge pressure too high

    First,

    We do need more information about your system to be able to assist you....

    Secondly,
    To me, 300 PSI head pressure sounds absolutely normal but this will depend on the refrigerant used and what system we are looking at.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: discharge pressure too high

    Please, tel us saturation temperatures instead of pressure, also subcooling and superheat. Then, air or water temperatures in and out of evaporator and condenser.

  4. #4
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    331
    Rep Power
    17

    Re: discharge pressure too high

    Quote Originally Posted by zahar View Post
    hello everybody...

    i'm new in refrigeration so i want to know why the discharge pressure is to high even if i run only 1 compressor.the pressure is 50 psi suction & 225 psi discharge,if i run 2 compressor,suction pressure is the same value but discharge will go higher to 300 psi.can you help me...
    We certianly need more info as others have stated. Sounds like you have a tandem system with a single circuit condenser?

  5. #5
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,094
    Rep Power
    23

    Re: discharge pressure too high

    High head press is not caused by the compressor if thats any help. Check charge, evap load and firstly the condenser, then expansion valve

  6. #6
    zahar's Avatar
    zahar Guest

    Re: discharge pressure too high

    thank you,i will check my chiller as you just mention.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: discharge pressure too high

    First you need to convert head pressure to saturated condensing temperature (SCT) using a pressure temperature (P/T) chart. Then you need to determine the temperature of the air entering the condenser. The difference between these two temperatures (condenser TD) should be 20-35F/11-19.5K. If the TD is in this range, then the pressure is normal.
    Last edited by Gary; 16-02-2008 at 06:27 PM.

  8. #8
    Join Date
    Nov 2006
    Location
    Scotland
    Age
    43
    Posts
    85
    Rep Power
    18

    Re: discharge pressure too high

    Hey buddy,looks like you getting answers from all over here.Follow the advice given,but do efficiency tests on the compresors just to be sure,they are the heart of the system after all.Then just take it from there....hope it helps...

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 02:25 PM
  3. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  4. cooling &freezing comp.
    By afeef in forum Industrial Compressors
    Replies: 25
    Last Post: 15-12-2006, 10:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •