Results 1 to 45 of 45
    west midlands
    98
    Capacity control
    Hello I was asked a question on a mock exam paper,and I am unsure of the correct answer.
    The question was Capacity control of a screw compressor is generally accomplished by:
    (a) Hot gas bypass
    (b) throttling the suction vapour
    (c) Cylinder unloading
    (d) sliding valve
    I did not get this correct,and i am unsure still.
    I think it might be (a) though.
    sparrow
    Aug 2003
    Netherlands
    49
    620
    Re: Capacity control
    The correct answer I think is (d) sliding valve.
    11,025
    Hi Sparrow, if you do a Google on the subject you will find a wealth of information on the different methods of capacity control available.
    Here's a starter for you
    http://www.emersonclimate.com/images...orBrochure.pdf
    Nov 2006
    63
    392
    Definately "D"
    Ian
    Feb 2007
    2,473
    I always been know to favour "D" or "DD"s and I won't change my mind because of this question
    11,025
    They go up to Js and Ks now I believe
    Aug 2005
    5,302
    Quote Originally Posted by Brian_UK
    Isn't that sort of overkill Brian?
    west midlands
    98
    Talking Re: Capacity control
    Brian, thanks that was just the ticket, nice one
    west midlands
    98
    Just as an after thought and because I keep coming accross this (Throttling the suction vapour)
    (A) What is it?
    (b) What is its role and how is it done,and why?
    Sparrow
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Mar 2007
    394
    Hello sparrow
    I hope I`m correct when I say that throttling the suction vapour is a process by which the vapour in the suction line is altered by means of a variable orifice situated closest to the suction port of the compressor. The concept of the orifice (valve) is similar to that of an EEV, that is a metering device, which will alter the saturation temp within the evap. by causing a pressure drop across itself.
    I hope that this will help you
    west midlands
    98
    Quote Originally Posted by TRASH101 View Post
    Hello sparrow
    Hello Trash, EEV? Why could we not just use a standard TEV or similar? does it have to be very specific, could we not just use a solonoid valve to allow the flow limitations into the TEV.
    Sorry to be a pain.
    TRASH101's Avatar
    Mar 2007
    394
    Furthermore Hot Gas Injection can be used in 2 ways (maybe more).
    1 injected after the expansion device so as too reduce the liquid content in the evap by a small amount of volume displacement and a lot by dumping loads of energy into the evap.
    2 injected after the evap. so as to condition the suction vapour without such an impact on the evap.
    sorry If this is a little vague but I would have to read up on this to get into the nitty gritty.
    Whats the slide valve then and all this d ,dd ,j & k
    sounds more like cup sizes to me?
    Aug 2007
    Adelaide Australia
    70
    562
    Hi Trash
    If you throttle the suction to a screw it will unload by adjusting the position of the slide valve as in normal operation.
    Sparrow
    D is definitely the correct answer. There is also another way that was not listed and that is to use a VF drive on the motor. This way the slide valve stays in the fully loaded position and does not slide back and forward causing wear.
    Hot gas bypass valve is for starting the compressor if the motor is a bit small. It opens and equalizes the suction and discharge so the compressor does not have to push against discharge pressure.
    A hot gas bypass can be used on a screw but not for cpacity control, it would be used where the suction can drop very quickly and then increase just a quickly, the compressor cannot unload quick enough and could trip. Also when the load comes back the compressor cannot load up quick enough. I have see this system on Carbo Coolers in a softdrink canning operations.
    Cylinder unloading is for a recip compressor.
    Hope this helps
    Paul
    Mar 2006
    Philippines
    124
    I think a,b,c,d are all incorporated in the process of capacity control.
    During unloading the slide valve will pull by the hydraulic cylinder it means the effect is throtling the suction, and if the capacity is at the minimum then the hot gas will blow at the suction to mentain the compressor running.
    regards
    TRASH101's Avatar
    Mar 2007
    394
    Hi again sparrow
    Didn`t mean to confuse you. The EEV is just a ropey example of how the throtteling valve works i.e. it works off "normally" a proportional signal which adjusts the valve position, rather like the valve/ actuator arrangement you would find on a low pressure hot water heater battery. The throtling valve must work in conjunction with a normal expansion device.
    If you used a solenoid in the system, especially the liquid line, for control modulation you would cause massive problems ,probabley destructive, as solenoids work as on/off devices.
    TRASH101's Avatar
    Mar 2007
    394
    cheers paulz
    but can you tell me the significance of all the letters
    i.e. dd,j etc..
    I`ve never come across a slide valve arrangement and would always opt. for variable speed drive for compressor operation when applicable.
    4,713
    D is the answer to the original question as many have already stated.
    Also consider the fact that on some Screw Comps you have a side load port. Increaseing volumetric gas flow further.
    Aug 2007
    Adelaide Australia
    70
    562
    Hi Trash
    If you don't know the significance of DD and all the way to J you must have led a sheltered life!!!!
    All screw compressors have slide valves, or at least all the ones I have worked on. You might want to Google Screw Compressors and all will become clear.
    Paul
    TRASH101's Avatar
    Mar 2007
    394
    ah curse you paul for so easily identifying my cotton wool wardrobe.
    Its a case of too much AC not enough fridge I`m afraid. Seldom, in 10 yrs, have I worked on anything that wasn`t hermetically sealed. Have browsed for info and can appreciate the design (man/auto ported by-pass), but the lettering is still eluding me. Are they the graduation markers on the slide for manual setting ? surely not.
    5,668
    I've got to put you out of your misery Trash. Have a look at this - but don't get overly excited
    TRASH101's Avatar
    Mar 2007
    394
    Thanks Brian
    I am going home to advise my good lady wife that if she wants to stop her screw unloading before the correct process reqiurements are met she should reduce from e to c.
    p.s. will you be able to put me out of my misery when she reciprocates (that will entail massive HEATed Rejection and the compression of my non condesables ?)
    west midlands
    98
    Trash you need some serious help lol, as for the young lady surely just a vest would suffice here.
    or was i expecting a little more?
    Sparrow
  23. #23
    Nov 2007
    Dubai
    52
    12
    hi
    slide valve
  24. #24
    Aug 2007
    Adelaide Australia
    70
    562
    Trash just remember a good fridgie always takes care of his noncondensables.
    Paul
  25. #25
    Croatia
    68
    2,261
    Hi, Sparrow
    Quote Originally Posted by sparrow View Post
    (a) Hot gas bypass
    (d) sliding valve
    sparrow
    During start we can utilize (a) if it's installed, to reduce starting torque - easier start....also sometimes (after long shut down) we have to start the screw compressor with throttled suction stop valve thus (b) too,
    ...as we do not have any pistons and cylinders on screw compressors we cannot use (c) at all,
    ....normal operation capacity control of screw compressors is obtained by sliding valve (d) controlling opening or closing suction port,
    ...on new compressors we have also Vi slide valve to control the opening of discharge port, mainly, but having some affect also to suction port...according to relation between suction and discharge pressure...some of them with automatic some with manual positioning...
    Best regards, Josip
  26. #26
    west midlands
    98
    Josip, hi sorry still trying to work all of that out, What you are saying is that quite possibly three of the answers could of been selected but for differing reasons? I think the answer they were looking for was D.
    I know you are indeed very bright and so have many others in this thread proven themselves so, could i get a better understanding on the coefficient performance on refrigeration and heat pumps.
    I have this thus far
    The coefficient of performance, or COP (sometimes CP), of a heat pump is the ratio of the output heat to the supplied work or
    where Q is the useful heat supplied by the condenser and W is the work consumed by the compressor.
    According to the first law of thermodynamics, in a reversible system we can show that Qhot = Qcold + W and W = Qhot - Qcold, where Qhot is the heat taken in by the cold heat reservoir and Qcold is the heat given off by the hot heat reservoir.
    Therefore, by substituting for W,
    where Q is the useful heat supplied by the condenser and W is the work consumed by the compressor. (Note: COP has no units, therefore in this equation, heat and work must be expressed in the same units.)
    Therefore, by substituting for W,, where Thot and Tcold are the temperatures of the hot and cold heat reservoirs respectively.
    It can also be shown that COPcooling = COPheating - 1. Note that these equations must use the absolute temperature, such as the Kelvin scale.
    A geothermal heat pump heating a building and operating at COPheating 3.5 provides 3.5 units of heat for every unit of energy it consumes (e.g. such a heat pump consuming 1 kW would provide 3.5 kW to heat a building). The "provided" heat comes from both the heat source and the input energy, so this does not mean that the heat source is cooled at a rate of 3.5 kW. The COP of heat pumps seems to compare very favorably with high-efficiency gas-burning furnaces (90-99% efficient), and electric heating (100%), but the full costs of the energy consumed must be considered, and energy from gas is typically much less expensive than that from electricity. Even so, a heat pump of COPheating 3.5, such as in the example above, could be less expensive to use than even the most efficient gas furnace.
    A heat pump (air conditioner) cooling a building and operating at COPcooling 2.0 removes 2 units of heat for every unit of energy it consumes (e.g. such an air conditioner consuming 1 kW would remove heat from a building's air at a rate of 2 kW, partly through cooling and partly through dehumidification).
    COPheating applies to heat pumps and COPcooling applies to air conditioners or refrigerators.
    Is this the standard accepted on heat pumps?
    Sparrow
  27. #27
    Aug 2005
    5,302
    D would have been the conventional answer. What Josip was trying to tell you is that you will find other types of unloading on screw compressors.
    In fact you could go so far as to say there is a fifth answer: variable speed operation.
    Some screw compressors use solenoid valves to open cylinder bores for by-passing suction gas also.
  28. #28
    Croatia
    68
    2,261
    Hi, Sparrow
    ...it was not my intention to make things harder to you, but US Iceman (Thanks Mike) repair my mistake...
    ...as English is not my mother tongue, sometimes I face problem to explain something clearly...., but here are some links where you will find very nice explanations...of COP, EER...
    http://www.canren.gc.ca/prod_serv/in...=169&PgId=1023
    http://www.heatpumpcentre.org/About_...erformance.asp
    http://tva.apogee.net/res/rehpeff.asp
    http://tva.apogee.net/res/rehcop.asp
    http://tva.apogee.net/res/reheer.asp
    Hope this is of some help..
    Best regards, Josip
  29. #29
    Aug 2005
    5,302
    Happy to help Josip. I don't think you made a mistake at all. I think the confusion was based on sparrow looking for one answer, and you correctly told him more than he was prepared for.
  30. #30
    west midlands
    98
    Yes I concur the reason for specifically looking for one definitive answer is that when I take the exam, and the computer is linked directly to the city and guilds board, they generally do tend to laugh off any students, multi selected answers.
    Don’t get me wrong if I could put more than one in I would be happy to do so.
    This action will invalidate my submitted attempt, and hence no cigar would be the outcome.
    The cop info you supplied Josip was the business, I was able to discuss with confidence today the findings.
    I have now moved into designing a wiring diagram for a pump down system.
    Knowing why each component follows directly after the previous one is also very important, Question 1
    Would I be able following the thermostat, be rite in thinking that I could connect to a solenoid valve? Or would one have to go directly to the compressor, in order to move the refrigerant?
    Sparrow
  31. #31
    5,668
    Question 1
    Sparrow
    Providing that the compressor has an LP (low pressure) switch fitted, then you can control the SV with a thermostat to effect pump down. If you position the SV close to the evaporator inlet then you effectively have all the liquid line to use for storage of the refigerant as well as the condenser (where no receiver is fitted).
    With long pipework runs you can get cycling on the LP switch at startup while the evaporator fills, but this can be overcome by delaying the compressor start for a couple of minutes after the SV is energised.
  32. #32
    west midlands
    98
    HI Frank is it me or is everyone a site moderator and more inportantly a general nice guy?
    Anyway thanks for you prompt reply, I have considered the information you have put forward, to this end I feel I should point out that the system has to have a liquid receiver incorporated also there is Surge pot, now I was under the misconception that this little piece of necessary equipment was called an accumulator.
    My Tutor advises me differently, anyhow I have to incorporate not only the low pressure switch, I also have the high pressure switch and as you point out the Sv just shy of the evaporator inlet. This little beauty must include my black rod defrost set up,again these do not trouble me too much as there is only a live feed to these just like a switch either on, on defrost cycle or not. (could they take being on for two hours?)
    Sparrow
  33. #33
    New Zealand
    80
    54
    The method I prefer for load control on screw compressors on new equipment is speed control. We find that range between 4 - 6 pole on the 50 Hz system gives quite an efficient and smooth operational profile. Below 4 pole it is considered that slippage could occur. The operational percentage between 6 pole being a 100 % , 4 Pole produces 48%. Many installations still use the slide as the means of control and is quite acceptable but once the capacity position reduces below 90% the overall efficiency begins to drop off quite rapidly. Suction throttle. This is used on plants where the compressors suction is at a common low pressure but the plant may have two or more operational evaporation requirements in the field , i.e. chillers and freezers . The plant suction will be maintained at a pressure in the freezer range but the evaporation on the chiller system held say 2 bar (30 psi) higher by being throttled via a BPV such as a Danfoss PM . Works OK by not all that efficient but initial costs sometimes makes it attractive.
  34. #34
    tinpoint's Avatar
    tinpoint Guest
    Re: new question
    An Rmo Observes A Gauge That Reads The Saturation Pressure Of A
    Refrigerant, If Chilled Water Is Being Circulated As The Cooling
    Meduim This Reading Can Best Be Used To Estimate:
    A. The Temperature Of Chilled Water Bieng Pumped To Spaces
    B. Chilled Water Temperature Return
    C. Cooling Tower Water Efficiency
    D. Condenser Water Flow Rate
  35. #35
    malaysia
    159
    (a) Hot gas bypass
    (d) sliding valve
    sparrow
    since it was an exam Q, i feel the educator is looking for answer D.
    however, in real life all the above is applicable in capacity ctrl.
    it has to do with the engineer's design concept & his/her selection of equipment.
    sometimes, the lowest capacity after unloading the compressor is still too high cap for the job, you have to introduce something else to stabilize the system.
    i feel, for exam, we have to answer smartly to fits the needs and not so much to our expertise.
  36. #36
    conrad's Avatar
    conrad Guest
    (a) Hot gas bypass
    (d) sliding valve
    sparrow
    tha answer is [d]
  37. #37
    Croatia
    68
    2,261
    Re: new question
    Hi, Tinpoint
    Quote Originally Posted by tinpoint View Post
    An Rmo is-
    a-Radar Management Officer
    b-Regional Medical Officer
    c-Responsible Managing Officer
    d-Risk Management Office/Officer
    e-Resident Medical Officer
    f-Records Management Official
    g-someone else
    Is this question from some exam to confirm/denied your answer or maybe a question for RE members
    What do you think we can estimate with this reading?
    Best regards, Josip
  38. #38
    Feb 2008
    Norway
    446
    I agrees definitely on this!
  39. #39
    rajaprabhu's Avatar
    rajaprabhu Guest
    The answer is Sliding Valve
  40. #40
    Sep 2005
    Atlanta Georgia USA
    80
    Have you guys seen screw capacity control be suction cut-off or hot gas bypass?
    I've only seen slide valves, port, and variable speed as cap control devices.
    I have see Vi control to minimize over compression.
  41. #41
    Feb 2009
    india
    (a) Hot gas bypass
    (d) sliding valve
    sparrow
    answe is d
  42. #42
    Feb 2009
    india
    correct answer is d
  43. #43
    west midlands
    98
    The method of compressor capacity control known as "suction valve lifting" is operated by
    (a) hydraulic oil pressure
    (b) changes in compressor discharge pressure
    (c) internal gearing connected to the compressor crankshaft
    (d) a transducer in the suction line
    I got this incorrect can someone shed some light please.
    Sparrow
    Always easy on the eye.
  44. #44
    TRASH101's Avatar
    Mar 2007
    394
    Quidvis Recte Factum Quamvis Humile Praeclarum.
  45. #45
    west midlands
    98
    whoa, that's more like it trash thanks.
    Sparrow
  1. Frick Quantum LX Compressor control panel: Capacity Control Screen
    By screw_geek in forum Industrial Compressors
    Last Post: 15-06-2008, 06:47 AM
  2. capacity control for 100% fresh air dx system
    By coztemur in forum Air Conditioning
    Last Post: 26-03-2007, 07:52 PM
  3. Capacity achievement
    By Hemant Anand in forum Industrial
    Last Post: 18-12-2005, 01:18 AM
  4. Capacity Control Head
    By abbasi in forum Fundamentals
    Last Post: 07-05-2005, 12:25 PM
  5. New Capacity Control Solution
    By embrown in forum New Technologies
    Last Post: 30-12-2003, 01:33 PM