    Capacity control



    Hello I was asked a question on a mock exam paper,and I am unsure of the correct answer.

    The question was Capacity control of a screw compressor is generally accomplished by:

    (a) Hot gas bypass

    (b) throttling the suction vapour

    (c) Cylinder unloading

    (d) sliding valve

    I did not get this correct,and i am unsure still.

    I think it might be (a) though.

    sparrow



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    621
    Rep Power
    21

    Re: Capacity control

    The correct answer I think is (d) sliding valve.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Capacity control

    Hi Sparrow, if you do a Google on the subject you will find a wealth of information on the different methods of capacity control available.

    Here's a starter for you
    http://www.emersonclimate.com/images...orBrochure.pdf
    Last edited by Brian_UK; 22-11-2007 at 12:22 AM. Reason: Spelling!
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    395
    Rep Power
    18

    Re: Capacity control

    Definately "D"

    Ian

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Capacity control

    I always been know to favour "D" or "DD"s and I won't change my mind because of this question
    Last edited by The Viking; 22-11-2007 at 01:21 AM.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Capacity control

    They go up to Js and Ks now I believe
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Capacity control

    Quote Originally Posted by Brian_UK
    They go up to Js and Ks now I believe
    Isn't that sort of overkill Brian?
    If all else fails, ask for help.


  8. #8
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Talking Re: Capacity control

    Quote Originally Posted by Brian_UK View Post
    Hi Sparrow, if you do a Google on the subject you will find a wealth of information on the different methods of capacity control available.

    Here's a starter for you
    http://www.emersonclimate.com/images...orBrochure.pdf
    Brian, thanks that was just the ticket, nice one

  9. #9
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Re: Capacity control

    Just as an after thought and because I keep coming accross this (Throttling the suction vapour)

    (A) What is it?
    (b) What is its role and how is it done,and why?

    Sparrow

  10. #10
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    397
    Rep Power
    18

    Re: Capacity control

    Hello sparrow

    I hope I`m correct when I say that throttling the suction vapour is a process by which the vapour in the suction line is altered by means of a variable orifice situated closest to the suction port of the compressor. The concept of the orifice (valve) is similar to that of an EEV, that is a metering device, which will alter the saturation temp within the evap. by causing a pressure drop across itself.

    I hope that this will help you

  11. #11
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Re: Capacity control

    Quote Originally Posted by TRASH101 View Post
    Hello sparrow

    I hope I`m correct when I say that throttling the suction vapour is a process by which the vapour in the suction line is altered by means of a variable orifice situated closest to the suction port of the compressor. The concept of the orifice (valve) is similar to that of an EEV, that is a metering device, which will alter the saturation temp within the evap. by causing a pressure drop across itself.
    Hello Trash, EEV? Why could we not just use a standard TEV or similar? does it have to be very specific, could we not just use a solonoid valve to allow the flow limitations into the TEV.

    Sorry to be a pain.
    Last edited by frank; 22-11-2007 at 02:42 PM.

  12. #12
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    397
    Rep Power
    18

    Re: Capacity control

    Furthermore Hot Gas Injection can be used in 2 ways (maybe more).
    1 injected after the expansion device so as too reduce the liquid content in the evap by a small amount of volume displacement and a lot by dumping loads of energy into the evap.

    2 injected after the evap. so as to condition the suction vapour without such an impact on the evap.

    sorry If this is a little vague but I would have to read up on this to get into the nitty gritty.

    Whats the slide valve then and all this d ,dd ,j & k
    sounds more like cup sizes to me?

  13. #13
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: Capacity control

    Hi Trash
    If you throttle the suction to a screw it will unload by adjusting the position of the slide valve as in normal operation.

    Sparrow
    D is definitely the correct answer. There is also another way that was not listed and that is to use a VF drive on the motor. This way the slide valve stays in the fully loaded position and does not slide back and forward causing wear.
    Hot gas bypass valve is for starting the compressor if the motor is a bit small. It opens and equalizes the suction and discharge so the compressor does not have to push against discharge pressure.
    A hot gas bypass can be used on a screw but not for cpacity control, it would be used where the suction can drop very quickly and then increase just a quickly, the compressor cannot unload quick enough and could trip. Also when the load comes back the compressor cannot load up quick enough. I have see this system on Carbo Coolers in a softdrink canning operations.
    Cylinder unloading is for a recip compressor.
    Hope this helps
    Paul

  14. #14
    Join Date
    Mar 2006
    Location
    Philippines
    Age
    53
    Posts
    124
    Rep Power
    19

    Re: Capacity control

    Hi,
    I think a,b,c,d are all incorporated in the process of capacity control.

    During unloading the slide valve will pull by the hydraulic cylinder it means the effect is throtling the suction, and if the capacity is at the minimum then the hot gas will blow at the suction to mentain the compressor running.

    regards

  15. #15
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    397
    Rep Power
    18

    Re: Capacity control

    Hi again sparrow

    Didn`t mean to confuse you. The EEV is just a ropey example of how the throtteling valve works i.e. it works off "normally" a proportional signal which adjusts the valve position, rather like the valve/ actuator arrangement you would find on a low pressure hot water heater battery. The throtling valve must work in conjunction with a normal expansion device.

    If you used a solenoid in the system, especially the liquid line, for control modulation you would cause massive problems ,probabley destructive, as solenoids work as on/off devices.

  16. #16
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    397
    Rep Power
    18

    Re: Capacity control

    cheers paulz

    but can you tell me the significance of all the letters
    i.e. dd,j etc..

    I`ve never come across a slide valve arrangement and would always opt. for variable speed drive for compressor operation when applicable.

  17. #17
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Capacity control

    D is the answer to the original question as many have already stated.
    Also consider the fact that on some Screw Comps you have a side load port. Increaseing volumetric gas flow further.
    Grizzly

  18. #18
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: Capacity control

    Hi Trash
    If you don't know the significance of DD and all the way to J you must have led a sheltered life!!!!

    All screw compressors have slide valves, or at least all the ones I have worked on. You might want to Google Screw Compressors and all will become clear.
    Paul

  19. #19
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    397
    Rep Power
    18

    Re: Capacity control

    ah curse you paul for so easily identifying my cotton wool wardrobe.

    Its a case of too much AC not enough fridge I`m afraid. Seldom, in 10 yrs, have I worked on anything that wasn`t hermetically sealed. Have browsed for info and can appreciate the design (man/auto ported by-pass), but the lettering is still eluding me. Are they the graduation markers on the slide for manual setting ? surely not.

  20. #20
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Capacity control

    Quote Originally Posted by TRASH101 View Post
    but the lettering is still eluding me. Are they the graduation markers on the slide for manual setting ? surely not.
    I've got to put you out of your misery Trash. Have a look at this - but don't get overly excited


  21. #21
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    397
    Rep Power
    18

    Re: Capacity control

    Thanks Brian

    I am going home to advise my good lady wife that if she wants to stop her screw unloading before the correct process reqiurements are met she should reduce from e to c.

    p.s. will you be able to put me out of my misery when she reciprocates (that will entail massive HEATed Rejection and the compression of my non condesables ?)

  22. #22
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Re: Capacity control

    Trash you need some serious help lol, as for the young lady surely just a vest would suffice here.

    or was i expecting a little more?

    Sparrow

  23. #23
    Join Date
    Nov 2007
    Location
    Dubai
    Age
    52
    Posts
    12
    Rep Power
    0

    Re: Capacity control

    hi
    slide valve

  24. #24
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: Capacity control

    Trash just remember a good fridgie always takes care of his noncondensables.
    Paul

  25. #25
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Capacity control

    Hi, Sparrow

    Quote Originally Posted by sparrow View Post
    Hello I was asked a question on a mock exam paper,and I am unsure of the correct answer.

    The question was Capacity control of a screw compressor is generally accomplished by:

    (a) Hot gas bypass

    (b) throttling the suction vapour

    (c) Cylinder unloading

    (d) sliding valve

    I did not get this correct,and i am unsure still.

    I think it might be (a) though.

    sparrow
    During start we can utilize (a) if it's installed, to reduce starting torque - easier start....also sometimes (after long shut down) we have to start the screw compressor with throttled suction stop valve thus (b) too,

    ...as we do not have any pistons and cylinders on screw compressors we cannot use (c) at all,

    ....normal operation capacity control of screw compressors is obtained by sliding valve (d) controlling opening or closing suction port,

    ...on new compressors we have also Vi slide valve to control the opening of discharge port, mainly, but having some affect also to suction port...according to relation between suction and discharge pressure...some of them with automatic some with manual positioning...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  26. #26
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Re: Capacity control

    Josip, hi sorry still trying to work all of that out, What you are saying is that quite possibly three of the answers could of been selected but for differing reasons? I think the answer they were looking for was D.

    I know you are indeed very bright and so have many others in this thread proven themselves so, could i get a better understanding on the coefficient performance on refrigeration and heat pumps.

    I have this thus far
    The coefficient of performance, or COP (sometimes CP), of a heat pump is the ratio of the output heat to the supplied work or

    where Q is the useful heat supplied by the condenser and W is the work consumed by the compressor.
    According to the first law of thermodynamics, in a reversible system we can show that Qhot = Qcold + W and W = Qhot - Qcold, where Qhot is the heat taken in by the cold heat reservoir and Qcold is the heat given off by the hot heat reservoir.
    Therefore, by substituting for W,
    The coefficient of performance, or COP (sometimes CP), of a heat pump is the ratio of the output heat to the supplied work or

    where Q is the useful heat supplied by the condenser and W is the work consumed by the compressor. (Note: COP has no units, therefore in this equation, heat and work must be expressed in the same units.)
    According to the first law of thermodynamics, in a reversible system we can show that Qhot = Qcold + W and W = Qhot - Qcold, where Qhot is the heat taken in by the cold heat reservoir and Qcold is the heat given off by the hot heat reservoir.
    Therefore, by substituting for W,, where Thot and Tcold are the temperatures of the hot and cold heat reservoirs respectively.



    It can also be shown that COPcooling = COPheating - 1. Note that these equations must use the absolute temperature, such as the Kelvin scale.
    A geothermal heat pump heating a building and operating at COPheating 3.5 provides 3.5 units of heat for every unit of energy it consumes (e.g. such a heat pump consuming 1 kW would provide 3.5 kW to heat a building). The "provided" heat comes from both the heat source and the input energy, so this does not mean that the heat source is cooled at a rate of 3.5 kW. The COP of heat pumps seems to compare very favorably with high-efficiency gas-burning furnaces (90-99% efficient), and electric heating (100%), but the full costs of the energy consumed must be considered, and energy from gas is typically much less expensive than that from electricity. Even so, a heat pump of COPheating 3.5, such as in the example above, could be less expensive to use than even the most efficient gas furnace.
    A heat pump (air conditioner) cooling a building and operating at COPcooling 2.0 removes 2 units of heat for every unit of energy it consumes (e.g. such an air conditioner consuming 1 kW would remove heat from a building's air at a rate of 2 kW, partly through cooling and partly through dehumidification).
    COPheating applies to heat pumps and COPcooling applies to air conditioners or refrigerators.

    Is this the standard accepted on heat pumps?

    Sparrow


  27. #27
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Capacity control

    Quote Originally Posted by sparrow
    Josip, hi sorry still trying to work all of that out, What you are saying is that quite possibly three of the answers could of been selected but for differing reasons? I think the answer they were looking for was D.
    D would have been the conventional answer. What Josip was trying to tell you is that you will find other types of unloading on screw compressors.

    In fact you could go so far as to say there is a fifth answer: variable speed operation.

    Some screw compressors use solenoid valves to open cylinder bores for by-passing suction gas also.
    If all else fails, ask for help.


  28. #28
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Capacity control

    Hi, Sparrow

    ...it was not my intention to make things harder to you, but US Iceman (Thanks Mike) repair my mistake...

    Quote Originally Posted by US Iceman View Post
    D would have been the conventional answer. What Josip was trying to tell you is that you will find other types of unloading on screw compressors.

    In fact you could go so far as to say there is a fifth answer: variable speed operation.

    Some screw compressors use solenoid valves to open cylinder bores for by-passing suction gas also.
    ...as English is not my mother tongue, sometimes I face problem to explain something clearly...., but here are some links where you will find very nice explanations...of COP, EER...

    http://www.canren.gc.ca/prod_serv/in...=169&PgId=1023

    http://www.heatpumpcentre.org/About_...erformance.asp

    http://tva.apogee.net/res/rehpeff.asp

    http://tva.apogee.net/res/rehcop.asp
    http://tva.apogee.net/res/reheer.asp

    Hope this is of some help..

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  29. #29
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Capacity control

    Happy to help Josip. I don't think you made a mistake at all. I think the confusion was based on sparrow looking for one answer, and you correctly told him more than he was prepared for.
    If all else fails, ask for help.


  30. #30
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Re: Capacity control

    Quote Originally Posted by US Iceman View Post
    Happy to help Josip. I don't think you made a mistake at all. I think the confusion was based on sparrow looking for one answer, and you correctly told him more than he was prepared for.
    Yes I concur the reason for specifically looking for one definitive answer is that when I take the exam, and the computer is linked directly to the city and guilds board, they generally do tend to laugh off any students, multi selected answers.

    Don’t get me wrong if I could put more than one in I would be happy to do so.
    This action will invalidate my submitted attempt, and hence no cigar would be the outcome.
    The cop info you supplied Josip was the business, I was able to discuss with confidence today the findings.
    I have now moved into designing a wiring diagram for a pump down system.
    Knowing why each component follows directly after the previous one is also very important, Question 1

    Would I be able following the thermostat, be rite in thinking that I could connect to a solenoid valve? Or would one have to go directly to the compressor, in order to move the refrigerant?

    Sparrow
    Last edited by frank; 27-11-2007 at 06:49 PM.

  31. #31
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Capacity control

    Quote Originally Posted by sparrow View Post
    Question 1

    Would I be able following the thermostat, be rite in thinking that I could connect to a solenoid valve? Or would one have to go directly to the compressor, in order to move the refrigerant?

    Sparrow
    Providing that the compressor has an LP (low pressure) switch fitted, then you can control the SV with a thermostat to effect pump down. If you position the SV close to the evaporator inlet then you effectively have all the liquid line to use for storage of the refigerant as well as the condenser (where no receiver is fitted).

    With long pipework runs you can get cycling on the LP switch at startup while the evaporator fills, but this can be overcome by delaying the compressor start for a couple of minutes after the SV is energised.

  32. #32
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Re: Capacity control

    HI Frank is it me or is everyone a site moderator and more inportantly a general nice guy?

    Anyway thanks for you prompt reply, I have considered the information you have put forward, to this end I feel I should point out that the system has to have a liquid receiver incorporated also there is Surge pot, now I was under the misconception that this little piece of necessary equipment was called an accumulator.

    My Tutor advises me differently, anyhow I have to incorporate not only the low pressure switch, I also have the high pressure switch and as you point out the Sv just shy of the evaporator inlet. This little beauty must include my black rod defrost set up,again these do not trouble me too much as there is only a live feed to these just like a switch either on, on defrost cycle or not. (could they take being on for two hours?)

    Sparrow

  33. #33
    Join Date
    Sep 2007
    Location
    New Zealand
    Age
    79
    Posts
    54
    Rep Power
    17

    Re: Capacity control

    The method I prefer for load control on screw compressors on new equipment is speed control. We find that range between 4 - 6 pole on the 50 Hz system gives quite an efficient and smooth operational profile. Below 4 pole it is considered that slippage could occur. The operational percentage between 6 pole being a 100 % , 4 Pole produces 48%. Many installations still use the slide as the means of control and is quite acceptable but once the capacity position reduces below 90% the overall efficiency begins to drop off quite rapidly. Suction throttle. This is used on plants where the compressors suction is at a common low pressure but the plant may have two or more operational evaporation requirements in the field , i.e. chillers and freezers . The plant suction will be maintained at a pressure in the freezer range but the evaporation on the chiller system held say 2 bar (30 psi) higher by being throttled via a BPV such as a Danfoss PM . Works OK by not all that efficient but initial costs sometimes makes it attractive.

  34. #34
    tinpoint's Avatar
    tinpoint Guest

    Re: new question

    An Rmo Observes A Gauge That Reads The Saturation Pressure Of A
    Refrigerant, If Chilled Water Is Being Circulated As The Cooling
    Meduim This Reading Can Best Be Used To Estimate:

    A. The Temperature Of Chilled Water Bieng Pumped To Spaces
    B. Chilled Water Temperature Return
    C. Cooling Tower Water Efficiency
    D. Condenser Water Flow Rate
    Last edited by tinpoint; 24-12-2007 at 11:07 PM.

  35. #35
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: Capacity control

    Quote Originally Posted by sparrow View Post
    Hello I was asked a question on a mock exam paper,and I am unsure of the correct answer.

    The question was Capacity control of a screw compressor is generally accomplished by:

    (a) Hot gas bypass

    (b) throttling the suction vapour

    (c) Cylinder unloading

    (d) sliding valve

    I did not get this correct,and i am unsure still.

    I think it might be (a) though.

    sparrow

    since it was an exam Q, i feel the educator is looking for answer D.

    however, in real life all the above is applicable in capacity ctrl.

    it has to do with the engineer's design concept & his/her selection of equipment.

    sometimes, the lowest capacity after unloading the compressor is still too high cap for the job, you have to introduce something else to stabilize the system.

    i feel, for exam, we have to answer smartly to fits the needs and not so much to our expertise.

  36. #36
    conrad's Avatar
    conrad Guest

    Re: Capacity control

    Quote Originally Posted by sparrow View Post
    Hello I was asked a question on a mock exam paper,and I am unsure of the correct answer.

    The question was Capacity control of a screw compressor is generally accomplished by:

    (a) Hot gas bypass

    (b) throttling the suction vapour

    (c) Cylinder unloading

    (d) sliding valve

    I did not get this correct,and i am unsure still.

    I think it might be (a) though.

    sparrow
    tha answer is [d]

  37. #37
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: new question

    Hi, Tinpoint

    Quote Originally Posted by tinpoint View Post
    An Rmo Observes A Gauge That Reads The Saturation Pressure Of A
    Refrigerant, If Chilled Water Is Being Circulated As The Cooling
    Meduim This Reading Can Best Be Used To Estimate:

    A. The Temperature Of Chilled Water Bieng Pumped To Spaces
    B. Chilled Water Temperature Return
    C. Cooling Tower Water Efficiency
    D. Condenser Water Flow Rate
    An Rmo is-
    a-Radar Management Officer
    b-Regional Medical Officer
    c-Responsible Managing Officer
    d-Risk Management Office/Officer
    e-Resident Medical Officer
    f-Records Management Official
    g-someone else


    Is this question from some exam to confirm/denied your answer or maybe a question for RE members

    What do you think we can estimate with this reading?


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  38. #38
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Capacity control

    Quote Originally Posted by The Viking View Post
    I always been know to favour "D" or "DD"s and I won't change my mind because of this question
    I agrees definitely on this!

  39. #39
    rajaprabhu's Avatar
    rajaprabhu Guest

    Re: Capacity control

    The answer is Sliding Valve

  40. #40
    Join Date
    Sep 2005
    Location
    Atlanta Georgia USA
    Age
    69
    Posts
    80
    Rep Power
    19

    Re: Capacity control

    Have you guys seen screw capacity control be suction cut-off or hot gas bypass?

    I've only seen slide valves, port, and variable speed as cap control devices.

    I have see Vi control to minimize over compression.

  41. #41
    Join Date
    Feb 2009
    Location
    india
    Posts
    17
    Rep Power
    0

    Re: Capacity control

    Quote Originally Posted by sparrow View Post
    Hello I was asked a question on a mock exam paper,and I am unsure of the correct answer.

    The question was Capacity control of a screw compressor is generally accomplished by:

    (a) Hot gas bypass

    (b) throttling the suction vapour

    (c) Cylinder unloading

    (d) sliding valve

    I did not get this correct,and i am unsure still.

    I think it might be (a) though.

    sparrow
    answe is d

  42. #42
    Join Date
    Feb 2009
    Location
    india
    Posts
    17
    Rep Power
    0

    Re: Capacity control

    correct answer is d

  43. #43
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Re: Capacity control

    The method of compressor capacity control known as "suction valve lifting" is operated by

    (a) hydraulic oil pressure

    (b) changes in compressor discharge pressure

    (c) internal gearing connected to the compressor crankshaft

    (d) a transducer in the suction line

    I got this incorrect can someone shed some light please.

    Sparrow
    Always easy on the eye.

  44. #44
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    397
    Rep Power
    18

    Re: Capacity control

    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  45. #45
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Re: Capacity control

    whoa, that's more like it trash thanks.

    Sparrow
    Always easy on the eye.

Similar Threads

  1. Frick Quantum LX Compressor control panel: Capacity Control Screen
    By screw_geek in forum Industrial Compressors
    Replies: 17
    Last Post: 15-06-2008, 06:47 AM
  2. capacity control for 100% fresh air dx system
    By coztemur in forum Air Conditioning
    Replies: 5
    Last Post: 26-03-2007, 07:52 PM
  3. Capacity achievement
    By Hemant Anand in forum Industrial
    Replies: 8
    Last Post: 18-12-2005, 02:18 AM
  4. Capacity Control Head
    By abbasi in forum Fundamentals
    Replies: 11
    Last Post: 07-05-2005, 12:25 PM
  5. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 02:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •