During start we can utilize (a) if it's installed, to reduce starting torque - easier start....also sometimes (after long shut down) we have to start the screw compressor with throttled suction stop valve thus (b) too,
...as we do not have any pistons and cylinders on screw compressors we cannot use (c) at all,
....normal operation capacity control of screw compressors is obtained by sliding valve (d) controlling opening or closing suction port,
...on new compressors we have also Vi slide valve to control the opening of discharge port, mainly, but having some affect also to suction port...according to relation between suction and discharge pressure...some of them with automatic some with manual positioning...
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
Similar Threads
-
Frick Quantum LX Compressor control panel: Capacity Control Screen
By screw_geek in forum Industrial CompressorsReplies: 17Last Post: 15-06-2008, 06:47 AM -
capacity control for 100% fresh air dx system
By coztemur in forum Air ConditioningReplies: 5Last Post: 26-03-2007, 07:52 PM -
Capacity achievement
By Hemant Anand in forum IndustrialReplies: 8Last Post: 18-12-2005, 01:18 AM -
Capacity Control Head
By abbasi in forum FundamentalsReplies: 11Last Post: 07-05-2005, 12:25 PM -
New Capacity Control Solution
By embrown in forum New TechnologiesReplies: 19Last Post: 30-12-2003, 01:33 PM