Thread: NH3 Liquid pumps
20-11-2007, 12:13 AM #1
NH3 Liquid pumps
What is the purpose of a Q,min and Q,max orifice plate on a liquid ammonia pump?
20-11-2007, 01:00 AM #2
Re: NH3 Liquid pumps
This is to control the minimum and maximum flow rate of the pump to allow optimum heat transfer, I think.
ian
20-11-2007, 01:43 AM #3
The q min is to ensure proper cooling of the motor and for general lubrication of the pump parts. The q max is an overload preventor.
20-11-2007, 01:46 AM #4
See page 4 of the document from this link:
http://hantech.com/documents/PDF/HP237.pdf
Hope that clears up the questions.If all else fails, ask for help.
20-11-2007, 01:54 AM #5
Minimum flow for cooling the electrical motor or for cooling the mechanical seal. Maximum flow for pump prime. At high flow the pump can loose prime.
Luiquid line vibration and liquid hammer
By Infinity in forum Trouble ShootingReplies: 12Last Post: 09-02-2007, 10:22 PM -
Ammonia Liquid Pumps
By nh3wizard in forum NH3Replies: 8Last Post: 05-09-2006, 07:48 PM -
Liquid line for multi evaporators
By Kevin Yeo in forum Supermarket RefrigerationReplies: 1Last Post: 29-12-2005, 02:29 PM -
Parker levels in ammonia systems
By Friobernal in forum IndustrialReplies: 3Last Post: 04-08-2005, 03:46 PM