Daikin lift pump
Hi,
Just powered up a new FFQ60B and after 10 seconds or so after turning on isolator the familiar sound of the lift pump was constantly coming from the unit, with controller off.
Switched on at controller (brc152d) no fault showed, ran on fan only, high and low speeds and swing worked fine, lift pump still running.
Disconnected lift pump from pcb (X25A) switched back on fan only, ran fine and no noise from pump.
I have left the indoor isolator off but outdoor is powered up to warm crankcase before running when I go back friday to commission.
Just wondering if anyone has had this before on an FFQ, I am guesing the float switch could be stuck or I have a faulty lift pump? Is it fairly easy to get at these?
Cheers
-
14-11-2007, 10:14 PM #2
Re: Daikin lift pump
Hi Slim, never had that problem with that unit,but the float and the pump arent to easy to get to, total strip down is pritty much whats needed, at least it wont be full of water to drip over you and the floor,..
-
15-11-2007, 08:32 PM #3
Re: Daikin lift pump
Yea just found the disassembly guide and it is drain pan removal to get to it.
Although looking at the piping side of the cassette (from access door in ceiling void) it looks as if there is a removable panel fixed with self tappers to to get at the pump, or is that just how the casing is held together, as normally they are spot welded??
Cheers
-
15-11-2007, 09:09 PM #4
Re: Daikin lift pump
I may be wrong but after a quick look at the pdf manual I think that things aren't that bad. I have stripped out this type before and the drain pan should stay in.
Switch off, remove the fan/air inlet cover and then remove the fan blade.
In the corner, where the pump is, there is a plate held in with two or four screws. Take that off and the pump is behind.
You might find the pump holding screws a bit fiddly to get at but not too bad.
The float switch is also accessible.
Good luck with it.
Just a thought, how long does the pump keep running for? They can start up when the unit is first started so maybe it is waiting for a 'time-out'.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
15-11-2007, 11:29 PM #5
Re: Daikin lift pump
Thanks for that info Brian.
The pump was only powered for about 2 mins then I first cut the power as I have never had this with any cassette before.
How long ae you talking for this time-out? It will be worth trying first in the morning.
-
16-11-2007, 12:21 AM #6
-
16-11-2007, 06:29 PM #7
Re: Daikin lift pump
Powered back up today and the pump run for 9 1/2 minutes then cut out. Happy Days
-
16-11-2007, 07:11 PM #8
Re: Daikin lift pump
Glad to hear that all is well, thanks for the update.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
19-11-2007, 10:30 PM #9
Re: Daikin lift pump
the float switch only operates on high limit causing an a3 fault.the pump runs continuously on cooling mode and for 3 minutes after cooling mode
-
13-07-2009, 08:03 PM #10
Re: Daikin lift pump
i really hate changin this type of pump- aaagghhhh
-
13-07-2009, 11:12 PM #11
Re: Daikin lift pump
You mean that wet feeling running down your sleeve ?
Brian - Newton Abbot, Devon, UK
Retired March 2015
Similar Threads
-
liquid ammonia pump calvitation
By Kathleen in forum Trouble ShootingReplies: 23Last Post: 20-05-2011, 02:18 AM -
Daikin not working... many problems
By stankovicv in forum Air ConditioningReplies: 26Last Post: 11-12-2010, 10:01 AM -
Help with condensor pump
By Bakerbj in forum Air ConditioningReplies: 23Last Post: 14-06-2009, 12:39 AM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
Domestic VRF heat pump?
By electronicsuk in forum Heat PumpsReplies: 8Last Post: 30-10-2007, 08:53 AM