    Power required in a compressor



    Hi all,

    Definitely i know nothing about refrigeration!!!

    Today i was reading a brochure of a manufacturer of compressors, when i realised that, for the same compressor, when the evaporating temperature becomes lower, the Refrigerant capacity becomes lower too (OK iīm agree looking a P-h diagram) but the power required also decreases... WHY??

    My first thought was; ok it is a semi-hermetic compressor, letīs look open compressors, and happens the same

    Please an answer!!! (I have to come back to school )

    Regards



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    As the evaporating temperature rises, the pressure in the low side of the system rises. With higher pressure pushing it, more refrigerant vapor is forced into the cylinder on each downstroke of the piston, thus the compressor capacity is increased. Since the compressor is doing more work (pumping more refrigerant vapor), more energy is required.
    Last edited by Gary; 06-02-2003 at 06:18 AM.

  3. #3
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    As Gary notes, the compressor must compress greater refrigerant mass at higher evaporator pressures. Not only must the compressor work harder, it also pumps more pounds of refrigerant.

    It is also worth noting that the fact a compressor consumes less power at lower suction pressures does not mean it will operate more efficiently at lower suction pressures. In fact, the opposite will be the case if the compressor isn't being overloaded.
    Prof Sporlan

  4. #4
    Join Date
    Dec 2002
    Location
    Malaysia
    Age
    59
    Posts
    86
    Rep Power
    22
    Dear Friobernal,

    To further get what Gary and the Prof had explained , just go to any compressor manufacturer's website e.g.

    http://www.bitzer.de or
    http://www.bock.de
    or
    grasso or copeland

    Download their compressor selection software - select a compressor - and then vary the evaporating temperature say, from -30 to 0 ( depending on the operating envelope ) and at each Tevap , record down the 1. Refrigeration Capacity, Power required and the Mass Flowrate and you will see the trend. ( Fix the condensing temp and other parameters i.e subcool,superheat etc )

    Also the P-h diagram appears to show that if the Tevap is lowered , the delta H of the compressor increases and this gives the false impression that the compressor power intake is higher. But then :

    Power required by the compressor is proportional to the product of 'delta H of the compressor ' and ' the mass flowrate '

    ( delta H of compression = ideal work of compression)

    And from your observation of the data you have recorded, you will find that the mass flowrate - kg/s- ( due to the higher specific volume m3/kg) gets lower as the T evap decreases.

    If you actually plot this power curve, you will find that at very low and very high evaporating temperatures, the power required is low and therefore there is a peak between these extremes. In reality. manufacturers do not make compressor to cover such a wide range of loads.

    Hope this helps !









Similar Threads

  1. Replies: 2
    Last Post: 01-01-2011, 03:57 AM
  2. compressor horse power
    By ewart in forum Industrial Compressors
    Replies: 9
    Last Post: 27-07-2009, 05:39 PM
  3. help required in locating expansion valve power head
    By Tejbir Singh in forum Trouble Shooting
    Replies: 10
    Last Post: 10-12-2004, 02:38 PM
  4. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 10:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •