    Diversity Factor



    Hi Everyone

    Heat Pump VRF 2 pipe, large shop, lots of self contained fridge cabinets (condensing indoors)

    Am using diversity factor of total x 0.85.

    Does anyone think this is about right?

    Thanks folks



  2. #2
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Diversity Factor

    Thanks everyone for the informed and helpful responses to this exciting thread.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Diversity Factor

    Yes, it does seem to have fallen on sad times doesn't it?

    Hopefully it will get picked up soon.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2008
    Location
    Lancs - UK
    Age
    67
    Posts
    30
    Rep Power
    0

    Re: Diversity Factor

    When you say total, I take it you have either calculated the total heat rejection from your equipment or you are working on manufacturers data ??

  5. #5
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Diversity Factor

    ypou need to calcualate the peak loa of the building as a whole and size it accordingly.

    Wetting your thumb in the air and picking 85% is simply a guess. Good luck.
    Take the V out of HVAC and you are left with a HAC job

  6. #6
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Diversity Factor

    Peak load x 0.85

  7. #7
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Diversity Factor

    Be carefull with Relative Humidity in the area of the shop with the cabinets & integral condensers.
    I have had to troubleshoot a number of shops with this setup over the years with multi split systems & VRF systems installed.
    The problem is the integral condensers only produce sensible heat.
    The a/c is constantly dehumidifying & the RH gets very low , like 30 % RH & then the indoor units are stopping cooling 1/2 the time on coil frost prevention. Then the room temperature get too hot because the indoor units only cooling 1/2 the time & RH still stays around 30%.
    The inverter split systems or VRF systems monitor the suction pressure / evaporating temp & because its very low due to the low RH room air on coil the outdoor unit slows down the compressor to raise the suction pressure to match target evaporating temp.
    This results in poor cooling performance at all the indoor units.

    The lowest indoor operating on coil WB temp for most split systems & VRF systems is 15 deg C WB & for sure the WB temp in the area of the shop with integral condensers will be lower than 15 deg C unless you address this issue.

    Really for this application diversity is not the most important issue as greater efficency savings can be achieved by using remote condensers for the cabinets & then the SH ratio is within the operating range of the split or VRF systems.

    Did you consider using heat recovery vetilation on your project ?
    With 12 months of the year cooling requirement & free cooling available for more than 6 months of the year with fresh air large energy savings to be made.

  8. #8
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Diversity Factor

    Very helpful post Thermatech, thanks.

    Had not considered heat recovery but makes a lot of sense.

    Remote condensers are not really an option as the shop is using stand alone cabinets, I wonder if these can be modified.

    They also have a large kitchen and it's all open plan. The kitchen is not very well vented, either.

    They're spending a FORTUNE on electricity.

Similar Threads

  1. U Factor
    By Samarjit Sen in forum Fundamentals
    Replies: 2
    Last Post: 03-06-2007, 03:53 AM
  2. R-22 to R-502 Capacity correction factor?
    By The MG Pony in forum Refrigerants
    Replies: 8
    Last Post: 23-04-2007, 04:04 AM
  3. Unit cooler rating factor
    By nh3simman in forum Fundamentals
    Replies: 4
    Last Post: 17-03-2007, 02:58 PM
  4. power factor correction
    By marley821 in forum Technical Discussions
    Replies: 4
    Last Post: 06-05-2006, 08:29 PM
  5. Looking for "K" factor and "U" factor tables
    By mayot in forum Fundamentals
    Replies: 1
    Last Post: 03-02-2006, 09:19 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •