    hi, guys in split a/c packages were are the filter/driers normally located also expansion device



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: expansion device location on split a/c systems

    On most new split ac's there's no filter/drier anymore. Expansion device is different for each brand! Could be indoors and outdoors, either lev, tev (or what ever els they call it) or cap.

  3. #3
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: expansion device location on split a/c systems

    Usually in the outdoor unit behind the compressor, ie above the service valves. They normally don't have a drier either, just a strainer.
    Large ducted ones or multi split units have them in the indoor unit sometimes though.

  4. #4
    Join Date
    Aug 2007
    Location
    ENGLAND
    Posts
    63
    Rep Power
    17

    Re: expansion device location on split a/c systems

    hi, paul h
    if the expansion device is in the outdoor unit would this make the discharge cold to touch and could it not pick up lots of heat by the time it gets to the evaperater
    cheers mate

  5. #5
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: expansion device location on split a/c systems

    Yes that is why the expansion line from the outdoor unit to the indoor is insulated (the small pipe)

    Ian

  6. #6
    Join Date
    May 2003
    Location
    Edmonton alberta Canada
    Posts
    95
    Rep Power
    21

    Re: expansion device location on split a/c systems

    The only place for the expansion device is at the evap drier at the outlet of condensor.
    Wes Maxfield

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: expansion device location on split a/c systems

    You really need to check the manufacturers technical manuals where they should show pipework layouts.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: expansion device location on split a/c systems

    Many have a mesh filter soldered inside the tube and not easy accesable.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    May 2003
    Location
    Edmonton alberta Canada
    Posts
    95
    Rep Power
    21

    Re: expansion device location on split a/c systems

    all filter driers have a mesh filter in them but it is good refrigeration practice to install a drier in all systems even if the factory will not.
    Wes Maxfield

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: expansion device location on split a/c systems

    I know, but they only have a mesh filter, not a dryer.
    If you install a filter, then it will allways be soaking wet and it wil rust after a short time.

    If it's a HP -most common nowadays - ,then you just can't install a standard dryer.

    If you installed everything according to the right rules, then you don't need a dryer.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: expansion device location on split a/c systems

    Peter
    going on your comments there should be a filter drier in the liquid and suction line taking that most splits are fitted by people who do not know how to instal them properly in the first place.

    Who needs training its only two pipes that need connecting and they are different sizes which makes it easier still.

    Sorry folks but questions like this one make me wonder why some people are being allowed near kit like this if they do not know how it works.

    Ian

  12. #12
    Join Date
    May 2003
    Location
    Edmonton alberta Canada
    Posts
    95
    Rep Power
    21

    Re: expansion device location on split a/c systems

    Well a different part of the world you do different things here if you do not put in a drier you are not doing a proper job and i have never heard of a liquid line drier that will rust.
    Wes Maxfield

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: expansion device location on split a/c systems

    Wesmax, both lines in nowadays AC's are LP and especially the small one has the lowest temperature where you will fit your drier because it's not yet superheated but at evaporating temperature, so around 0°C.
    Your drier is mostly in steel, so it will rust.

    Same story for the return line, even if it's superheated, you wille encounter conditions where condensation can't be avoided.

    AC's units in your part of the world are the same as we use here and I never saw in a manual of an AC that they recommend a drier.
    Daikin nor Mitsubishi nor any other brand has other recommendations in another part of the world.
    Unless you can show me this.

    Installing driers in AC's to solve the problems caused only by the lack of experience of DIY'ers isn't the right way.

    As said, if you install it the right way and follow the proper procedures, you don't need a filterdryer and if it was needed, then I wonder why I have so less troubles with those we instaled over more then 20 years.

    Proper procedures are valid universall.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #14
    Join Date
    May 2003
    Location
    Edmonton alberta Canada
    Posts
    95
    Rep Power
    21

    Re: expansion device location on split a/c systems

    We are talking two completely different systems we install very few splits here and I have never installed one , here the splits aresold mostly in cpartments and condo units . The most common are the A coil in the furnace and 20 to 50 feet away outside is the high side liquid line is high pressure. The only time the suction line has a drier is if the compressor has had a burnout and the new one needs to be protected.
    Wes Maxfield

  15. #15
    Join Date
    Mar 2009
    Location
    idaho
    Age
    45
    Posts
    8
    Rep Power
    0

    Re: expansion device location on split a/c systems

    mitsubishi dosent allow dryers because the expansion valve is located in the outdoor unit and the liquid line is only 3 inches long you cant get a filter dryer small enough to fit in there and they dont make suction dryers that flow 2 ways so its not allowed .liquid dryers cause to much restriction on there design.

Similar Threads

  1. Pressure testing for leaks on split a/c systems
    By mrchatts in forum Air Conditioning
    Replies: 46
    Last Post: 08-04-2010, 10:02 AM
  2. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  3. location of the expansion valve
    By smpsmp45 in forum NH3
    Replies: 5
    Last Post: 28-09-2007, 11:00 AM
  4. Expansion device - Co2 cycle
    By MrReds in forum CO2
    Replies: 2
    Last Post: 19-07-2007, 03:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •