Results 1 to 5 of 5
Thread: oversized filter/drier
-
04-02-2003, 12:03 AM #1
oversized filter/drier
What would be the effects of an oversized drier in a cap tube system?
John K.
-
04-02-2003, 01:44 AM #2
my guess..............?
More refrigermerant!
That's all.
-
04-02-2003, 09:06 PM #3
Hi,
also additional subcooling of the liquid, which would increase the capacity of the capillary, again leading to flood back.
This previous statement is again dependant on the placement of the drier, with driers facing vertically up causing the greatest increase in subcooling.
Regards. Andy
-
05-02-2003, 02:17 AM #4Extra note
========
Assuming the added liquid line volume inadvertanlty results in an increased charge.
With a TEV, however, no problem...Prof Sporlan
-
06-02-2003, 12:28 AM #5
Thank you all for the info I don't know when but one day I will be able to answer someones question on the forum.
John K.
Similar Threads
-
oversized??
By bernie in forum CommercialReplies: 13Last Post: 07-04-2003, 03:15 PM