    oversized filter/drier



    What would be the effects of an oversized drier in a cap tube system?


    John K.

  2. #2
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    my guess..............?

    More refrigermerant!

    That's all.


  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi,
    also additional subcooling of the liquid, which would increase the capacity of the capillary, again leading to flood back.
    This previous statement is again dependant on the placement of the drier, with driers facing vertically up causing the greatest increase in subcooling.
    Regards. Andy

  4. #4
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Extra note
    ========

    Assuming the added liquid line volume inadvertanlty results in an increased charge.
    The key here is a capillary tube system is a critically charged system. If the filter-drier acts like a receiver, then you can have some problems.

    With a TEV, however, no problem...
    Prof Sporlan

  5. #5
    Join Date
    Jul 2002
    Location
    Stamford, CT USA
    Age
    46
    Posts
    74
    Rep Power
    22

    Smile

    Thank you all for the info I don't know when but one day I will be able to answer someones question on the forum.
    John K.