    condenser subcooling



    Does load affect condenser subcooling . I know a low condenser subcooling can mean low charge but I work with blast freezers , there is a intial big load and 16 - 20 hours later the load is small . would subcooling be different at the start , when there is a big load and increase as the load gets smaller or would it stay about the same



  2. #2
    Join Date
    May 2007
    Location
    NC
    Posts
    264
    Rep Power
    17

    Re: condenser subcooling

    If the the conditioned space is the same temps and outside temp increase....the gas will not condense as fast running through the coil.

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,094
    Rep Power
    23

    Re: condenser subcooling

    Yes - As the load drops off the subcooling will increase. Mainly due to the tev closing, reducing evap temp and press, this reduces the amount of refrigerant flow allowing more time to cool the condensing refrigerant.

  4. #4
    Join Date
    Jun 2005
    Location
    California
    Posts
    395
    Rep Power
    19

    Re: condenser subcooling

    Tesla is correct, as load deminishes so does the mass flow and condenser has more refrigerant

  5. #5
    Join Date
    Apr 2007
    Location
    canada
    Age
    58
    Posts
    29
    Rep Power
    0

    Re: condenser subcooling

    From what you guys are saying , to use condenser subcooling to check a possible low charge , there should be little or no load on the system ?

  6. #6
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: condenser subcooling

    No, you'd want full load, so it runs optimal when it's needed the most. Check motor amps too.
    The reciever can take care of the excess refrigerant when there's low load.

  7. #7
    Join Date
    Apr 2007
    Location
    canada
    Age
    58
    Posts
    29
    Rep Power
    0

    Re: condenser subcooling

    Thanks Paul . 10 - 15 degrees subcooling at full load and the sub cooling will increase as the load decreases

  8. #8
    Join Date
    Aug 2007
    Location
    UK
    Posts
    15
    Rep Power
    0

    Re: condenser subcooling

    Hi Claude11

    Is that in degrees F?

  9. #9
    Join Date
    Apr 2007
    Location
    canada
    Age
    58
    Posts
    29
    Rep Power
    0

    Re: condenser subcooling

    Is it's degrees F . ( half my equipment is canadian [metric] and half is American made [ standard units]

  10. #10
    Join Date
    Nov 2007
    Location
    Romania
    Age
    58
    Posts
    14
    Rep Power
    0

    Re: condenser subcooling

    Quote Originally Posted by claude11 View Post
    Does load affect condenser subcooling . I know a low condenser subcooling can mean low charge but I work with blast freezers , there is a intial big load and 16 - 20 hours later the load is small . would subcooling be different at the start , when there is a big load and increase as the load gets smaller or would it stay about the same
    ---------------------------------------------------
    About subcooling :

    When subcooling the liquid refrigerant before it enters the expansion valve the purpose is twofold:
    - to increase plant refrigeration capacity;
    - to prevent flash gas formation ahead of the
    expansion valve .
    Condensed refrigerant can be subcooled in diferent ways :
    - by dimensioning condensers in such a way that in addition to featuring the necesary condensing surface they also incorporate a subcooling section.In air cooled condensers however the achived effect is normaly insignificant .By expanding the condensig surface you can at best reduce the condensing pressure.
    - by installing internal heat exchangers thereby providing subcooling and suction gas superheating at the same time.

    A good value of subcooling is 3...6 of Celsius degrease.

    Good luck

  11. #11
    Join Date
    Nov 2007
    Location
    Romania
    Age
    58
    Posts
    14
    Rep Power
    0

    Re: condenser subcooling

    Quote Originally Posted by claude11 View Post
    Does load affect condenser subcooling . I know a low condenser subcooling can mean low charge but I work with blast freezers , there is a intial big load and 16 - 20 hours later the load is small . would subcooling be different at the start , when there is a big load and increase as the load gets smaller or would it stay about the same
    ---------------------------------------------------
    If you have a good condensing control the subcooling it will by ,with small diferences ,the same.

  12. #12
    Join Date
    Nov 2007
    Location
    Dubai
    Age
    52
    Posts
    12
    Rep Power
    0

    Re: condenser subcooling

    Hi
    can u provide the full readings and measurments u have.

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: condenser subcooling

    A subcooler incoporated in the condensor coil is not that effective because if flows to the receiver where it will change to its saturated condition.
    It's better to use an additional condensor mounted under the main condensor and where the liquid is coming from the receiver before it goes to the TEV's via an isolated liquid line.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Efficient Water-Source Condenser Design?
    By Enginerd in forum Fundamentals
    Replies: 4
    Last Post: 28-05-2007, 05:11 AM
  2. Subcooling
    By terryw in forum Supermarket Refrigeration
    Replies: 12
    Last Post: 07-03-2007, 10:53 AM
  3. Subcooling & Refrigerants
    By US Iceman in forum Fundamentals
    Replies: 40
    Last Post: 29-04-2006, 02:59 AM
  4. hot discharge air from C.U
    By ong in forum Fundamentals
    Replies: 48
    Last Post: 29-07-2005, 06:24 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •