    hi, called to a site 2 weeks ago,problem wit wall mount...found the main mcb tripped and a neutral/live fuses blown on outdoor board which feed indoor,..so replaced fuses and tirned it on and went bang again....so went to indoor disconnected ind fan and tried again qand everything worked...so replaced indoor fan... started unit worked for about 4 days and went again, replacewd condensate pump just in case... system ran for a week and went again...anybody any ideasrgrds phil



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: mitsu indoor problem

    Did you carefully check the power supply?

    If there is a poor connection on N line you can have a 'floating N' problem.
    Between earth & N there should be zero volts.
    But if there is a poor N connection in the power supply line then there will be some measurable voltage between E & N at the outdoor unit & or indoor unt power supply terminals & silly voltage on the L line.
    I have seen Mitsubishi split systems working with this problem 20 to 40 volts E to N. They may work for a week or two & then blow a board, some times the outdoor board & another time the indoor board.
    If the N is completely disconected then the problem is easy to spot & boards tend to blow on first startup.

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: mitsu indoor problem

    I had a problem like this some time ago. Found the geniuses that fitted the condensate pump had wired the live 240v onto the signal wire of the board thus blowing the outdoor fuses and boards.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: mitsu indoor problem

    You could also have a problem with condensate.

    Check that all of the pipework is inside the drip tray as stray drops of water will short out the electrics and be dried out by the time you are called to the problem

    As will a short charge. Frost builds up where the pipes enter the evap and then when the unit switches off the defrost just overflows and causes a short.

  5. #5
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    985
    Rep Power
    19

    Re: mitsu indoor problem

    Quote Originally Posted by philjd26 View Post
    hi, called to a site 2 weeks ago,problem wit wall mount...found the main mcb tripped and a neutral/live fuses blown on outdoor board which feed indoor,..so replaced fuses and tirned it on and went bang again....so went to indoor disconnected ind fan and tried again qand everything worked...so replaced indoor fan... started unit worked for about 4 days and went again, replacewd condensate pump just in case... system ran for a week and went again...anybody any ideasrgrds phil

    does the wall mount also have the "sub power pcb" in the indoor like on a few older mitsu ive seen? its a pig to get too,its behind the main pcb
    Paul


    "KEEP IT COOL"

  6. #6
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    263
    Rep Power
    18

    Re: mitsu indoor problem

    hi,yeah it has sub board at the back, capacitor for fan as well, sometings definitly shorting..thanks for the replies will have a look at those things

    rgrds phil

  7. #7
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    263
    Rep Power
    18

    Re: mitsu indoor problem

    hi, still no joy with this problem going back tomorrow...one of the fuse blew today and it was the live fuse instead of the both left a nasty scource aswell.. i checked the amps only drawing .5 amp....any ideas?

    rgds phil

  8. #8
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    985
    Rep Power
    19

    Re: mitsu indoor problem

    Quote Originally Posted by philjd26 View Post
    hi, still no joy with this problem going back tomorrow...one of the fuse blew today and it was the live fuse instead of the both left a nasty scource aswell.. i checked the amps only drawing .5 amp....any ideas?

    rgds phil
    this maybe a long shot,is the indoor fan blade clean?
    Paul


    "KEEP IT COOL"

  9. #9
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    263
    Rep Power
    18

    Re: mitsu indoor problem

    hi, just to let you know i think i got this thing sorted, countinued to go bang every day or so, i tried lowerring the fan speed,that was 2 weeks ago and still running so i imagine a relay is bunched on the pcb or something..

    cheers phil

  10. #10
    Join Date
    Oct 2007
    Location
    Colombo
    Age
    72
    Posts
    15
    Rep Power
    0

    Re: mitsu indoor problem

    Quote Originally Posted by philjd26 View Post
    hi, i checked the amps only drawing .5 amp....any ideas?

    rgds phil
    Hi,
    what is the fuse rating. It should be higher than the motor rated current. Even you say it is 0.5 Amps , I feel it is exceeding the rate of the fuse.What about the rpm. Is that correct?

Similar Threads

  1. Freezing back to comp (mitsu elec)
    By expat in forum Air Conditioning
    Replies: 14
    Last Post: 29-07-2007, 11:14 PM
  2. mitsu heavy inds remote display
    By dirker in forum Heat Pumps
    Replies: 1
    Last Post: 08-04-2007, 10:54 PM
  3. Mitsu Heavy Ind. Fault Codes...
    By Scooby in forum Air Conditioning
    Replies: 1
    Last Post: 08-12-2005, 09:37 PM
  4. Mitsu Heavy Industry
    By bobjob in forum Air Conditioning
    Replies: 1
    Last Post: 14-07-2005, 11:00 PM
  5. Mitsu
    By Abe in forum Air Conditioning
    Replies: 11
    Last Post: 05-01-2003, 03:19 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •