    Been on the daikin commisioning installlation and service course today. Spoke to the trainer about how to use the controller to look at the readings from the thermisters but i only managed to get the outdoor thermister readings (if that makes sense). I got it off going to 40 on the hardwired controller. Does anyone have a list of the codes that would be useful when at the controller such as the indoor thermisters as well because i figure that if i have them all then you would be able to look at the superheat and subcooling through the controller and what everelse is relevant...



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Daikin Hard wired controller

    Go to the Daikin website and download the Sky Air tech book - ESIE03-01SkyAir L.pdf

    You'll find most things in there.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: Daikin Hard wired controller

    Ok thanks brian..

  4. #4
    Join Date
    Mar 2007
    Location
    France
    Posts
    237
    Rep Power
    18

    Re: Daikin Hard wired controller

    Hello Marc
    To make a complete control you need a small controler called RSUK919: it's a mini-checker that read data between indoor and outdoor units for split/multi/sky air from r22 to r410a heat pump series...
    Maybe you can order it from your local supplier ?
    As far as i know you can only read indoor temperature through the wired remote...
    Regards
    cool#9

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: Daikin Hard wired controller

    Quote Originally Posted by cool#9 View Post
    Hello Marc
    To make a complete control you need a small controler called RSUK919: it's a mini-checker that read data between indoor and outdoor units for split/multi/sky air from r22 to r410a heat pump series...
    Maybe you can order it from your local supplier ?
    As far as i know you can only read indoor temperature through the wired remote...
    Regards
    cool#9

    Sounds good, il have a look for it.. how is it connected?...would you disconnect the controller and plug into that?

  6. #6
    Join Date
    Mar 2007
    Location
    France
    Posts
    237
    Rep Power
    18

    Wink Re: Daikin Hard wired controller

    Am i the first one to speak about this device ?
    Well it's simple you just plug on 1/2/3 terminals and check either indoor or outdoor unit. No battery is needed. There are two ways to connect; 1 for r22/r407c series and 1 for r410a depending on the power supply (1/3 or 1/2).
    You can also connect it to a bigger checker via a little interface and helped by a sofware to do recording, monitoring for harder diagnosis...
    See the picture !
    Regards
    cool#9
    Last edited by cool#9; 09-10-2007 at 05:16 PM.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin Hard wired controller

    Can't say that I've seen one - but then again, I use the big Service Checker.

  8. #8
    Join Date
    Mar 2007
    Location
    France
    Posts
    237
    Rep Power
    18

    Re: Daikin Hard wired controller

    ok, but you maybe know the inverter analyser ?
    If not it's so simple to built, less than 15 euros of components !!!
    rgds

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin Hard wired controller

    Quote Originally Posted by cool#9 View Post
    ok, but you maybe know the inverter analyser ?
    If not it's so simple to built, less than 15 euros of components !!!
    rgds
    Yep - got one of those

  10. #10
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: Daikin Hard wired controller

    yeah i got one of those 38punds from daikin, theres not much to them is there but they are a handy little tool..

  11. #11
    Join Date
    Feb 2007
    Location
    north west
    Age
    36
    Posts
    244
    Rep Power
    18

    Re: Daikin Hard wired controller

    were else can you buy thos analyzers from any suggestions guy thanks alot

  12. #12
    Join Date
    Mar 2005
    Location
    Birmingham U.K.
    Age
    70
    Posts
    54
    Rep Power
    20

    Re: Daikin Hard wired controller

    Quote Originally Posted by cool#9 View Post
    Am i the first one to speak about this device ?
    Well it's simple you just plug on 1/2/3 terminals and check either indoor or outdoor unit. No battery is needed. There are two ways to connect; 1 for r22/r407c series and 1 for r410a depending on the power supply (1/3 or 1/2).
    You can also connect it to a bigger checker via a little interface and helped by a sofware to do recording, monitoring for harder diagnosis...
    See the picture !
    Regards
    cool#9
    Hi cool#9
    i use the the RSUK 0919 every other day but I never knew it could be used with the larger checker to monitor a unit over a timed period,
    Spoke to Daikin today they also did no know you could connect the RSUK to the checker.

    who supplied the software and interface?

    regards

    Bobjob

  13. #13
    Join Date
    Mar 2007
    Location
    uk
    Age
    51
    Posts
    122
    Rep Power
    18

    Re: Daikin Hard wired controller

    Hey cool9, I didnt even know the RSUK919 existed...!! nice one.

    Think its time to have a word with our supplier and invest in these for our service team, we already have the inverter checkers though.

  14. #14
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Daikin Hard wired controller

    Quote Originally Posted by cool#9 View Post
    Am i the first one to speak about this device ?
    Well it's simple you just plug on 1/2/3 terminals and check either indoor or outdoor unit. No battery is needed. There are two ways to connect; 1 for r22/r407c series and 1 for r410a depending on the power supply (1/3 or 1/2).
    You can also connect it to a bigger checker via a little interface and helped by a sofware to do recording, monitoring for harder diagnosis...
    See the picture !
    Regards
    cool#9
    I have also got one of these, don't use it all the time though.

    Good if you suspect a thermistor though.

  15. #15
    Join Date
    Mar 2007
    Location
    France
    Posts
    237
    Rep Power
    18

    Re: Daikin Hard wired controller

    Quote Originally Posted by bobjob View Post
    Hi cool#9
    i use the the RSUK 0919 every other day but I never knew it could be used with the larger checker to monitor a unit over a timed period,
    Spoke to Daikin today they also did no know you could connect the RSUK to the checker.

    who supplied the software and interface?

    regards

    Bobjob
    Hey Bobjob
    You need a special cable called MA/RA to connect the serial port of the service checker type 3 to the RSUK then after you can monitor.
    The main problem is to find the patch for the service checker software to read the RSUK that became an interface.
    A patch also exist to read directly from service checker type 3 to the new multisplit by the serial port on the small pcb.
    But ! using the RSUK alone is usually enough on split / multi / sky air...
    Note that is you have already MA/RA cable you can read a lot of outdoor unit like RZQ, RMX, 4MX_H via the serial port on the pcb...
    rgds
    cool#9

  16. #16
    Join Date
    Jul 2007
    Location
    Finland
    Age
    55
    Posts
    20
    Rep Power
    0

    Re: Daikin Hard wired controller

    Quote Originally Posted by cool#9 View Post
    Hey Bobjob
    You need a special cable called MA/RA to connect the serial port of the service checker type 3 to the RSUK then after you can monitor.
    The main problem is to find the patch for the service checker software to read the RSUK that became an interface.
    A patch also exist to read directly from service checker type 3 to the new multisplit by the serial port on the small pcb.
    But ! using the RSUK alone is usually enough on split / multi / sky air...
    Note that is you have already MA/RA cable you can read a lot of outdoor unit like RZQ, RMX, 4MX_H via the serial port on the pcb...
    rgds
    cool#9
    Hi!

    Where can i find patch (software) ?

    How do i use it?

    I already have M5/RA -cable which come in the Checker 3 box, did you mean that cable?

    (I've already test RSUK and Checker 3 but no succesfully)

    Basti.

  17. #17
    Join Date
    Nov 2007
    Location
    france
    Posts
    8
    Rep Power
    0

    Re: Daikin Hard wired controller

    Quote Originally Posted by cool#9 View Post
    Hey Bobjob
    You need a special cable called MA/RA to connect the serial port of the service checker type 3 to the RSUK then after you can monitor.
    The main problem is to find the patch for the service checker software to read the RSUK that became an interface.
    A patch also exist to read directly from service checker type 3 to the new multisplit by the serial port on the small pcb.
    But ! using the RSUK alone is usually enough on split / multi / sky air...
    Note that is you have already MA/RA cable you can read a lot of outdoor unit like RZQ, RMX, 4MX_H via the serial port on the pcb...
    rgds
    cool#9
    Hello,

    Did this can read 5MXS90E ?

    TY
    DD

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 10:01 AM
  2. Electronic controller probes wired wrong
    By Electrocoolman in forum Trouble Shooting
    Replies: 3
    Last Post: 12-11-2007, 07:39 PM
  3. daikin remote controller setting list
    By knight rider in forum Air Conditioning
    Replies: 9
    Last Post: 21-05-2007, 10:10 PM
  4. daikin controller pdf
    By rbartlett in forum Air Conditioning
    Replies: 9
    Last Post: 29-12-2006, 07:39 AM
  5. Daikin controller question
    By THERMOACC in forum Air Conditioning
    Replies: 9
    Last Post: 10-03-2006, 11:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •