Results 1 to 10 of 10
Thread: Alco Expansion Valve
06-11-2007, 05:23 PM #1
Hi everyone,
This is my first post, so be gentle!
I'm having trouble locating a replacement Alco expansion valve. The details I have from it are LMCHF4L. It appears to have a heater on the bulb which is fitted inside a pocket on a suction accumulator.
The refrigerant was R12 and is now R413a.
Any help or info would be much appreciated.
06-11-2007, 05:52 PM #2
Re: Alco Expansion Valve
I don't recognize the model number but the description you gave leads to me to believe you have a liquid level control valve. Sporlan also had something like this called a Level Master.
The heated bulb simply allowed the TXV to open, which allowed liquid refrigerant to flow through the valve and replenish the liquid in the accumulator.
When the liquid level in the accumulator reached the bulb, the bulb then cooled off, which forced the valve to close.
I tried to find the Sporlan document on their website, but it is going through a update right now, so I can't post a link for you to read about this.
Hope that helps in some small way.
PS. Welcome to the RE forums.If all else fails, ask for help.
07-11-2007, 03:59 AM #3
Danfoss also make one it's a TEVA valve. It is basically a TEA 20,85 TX valve with a heater assisted power assembly and uses the same orifices ranging from 1 TR to 85 TR. These are generally used on NH3 but if you contact Danfoss they would be able to tell you if you can use it on R413a.
08-11-2007, 07:04 PM #4
This is a "thermo valves for liquid injection", from ALCO Catalog 15.30 very old, Feb 1972. Search what they do.
08-11-2007, 07:06 PM #5
The "heater" may be a coil from solenoids.
11-11-2007, 03:14 PM #6
Big mistake, not "thermo valves for liquid injection", Look here XXX.frigodesign.ru/sale/sporlan/LiquidLevelControl_Sporlan.pdf[/url]
22-11-2007, 10:07 PM #7
Hi the man to speak to is The Alco Tech/Sales Ian 07770586742
Tech Slave
01-12-2007, 03:34 PM #8
about that - Alco Expansion Valve
Did you try calling ALCO ? I have always found them incredibly helpful, especially the engineering dept.
PHM
02-12-2007, 09:04 PM #9
It is SPORLAN, not ALCO. is a liquid level control valve
03-12-2007, 05:42 PM #10
Thanks guys.
Jose, it is a SPORLAN valve and I found all the info on their website.
Expansion Valve Selection
By raviperumal in forum Technical SpeculationsReplies: 12Last Post: 17-02-2010, 09:58 AM -
Fitting an expansion valve question
By Larry2 in forum Air ConditioningReplies: 20Last Post: 08-04-2008, 04:17 PM -
expansion valve aint cold
By justinworne in forum Trouble ShootingReplies: 6Last Post: 26-07-2006, 10:52 PM -
I want to find detailed files about ALCO zz thermo expansion valve
By brightfu1 in forum FundamentalsReplies: 2Last Post: 07-09-2005, 03:07 PM -
pressure drop between expansion valve and distributor
By aygul in forum Technical SpeculationsReplies: 10Last Post: 22-01-2004, 09:47 AM