    Position of three way valve in CWS



    Why three way valve is installed on the return side of Chilled water systems and on the supply side of hot water systems. Best regards.



  2. #2
    Join Date
    Mar 2006
    Location
    dallas, texas
    Age
    75
    Posts
    108
    Rep Power
    19

    Re: Position of three way valve in CWS

    The standard practice of my company, Trane is for 2 way or three way valves to be on the outlet side of a liquid evaporator coil. The reason for this is to alleviate the chance of air accumulating in the coil when off cycle. i am sure their are a few other thoughts on this, but this is the biggest reason.

    regards

    bruce

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Position of three way valve in CWS

    Which type of valve are you asking about, diverting or mixing?

    Also, before or after the pump?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Position of three way valve in CWS

    The reason they are installed diverting in cooling systems is to ensure flow through the entire system. The only way to get the valves to mix is to install them, in the correct position, in the return line.

    To get the heating system to work correct, they have to be installed in the feeding line to get the return water to help "cool" the feeding line off a heating group in order to get the right temperature, since most system calculate the main feed temperature on outside temperature (a so called outside temperature dependend control) or on bassis of a calculated needed temperature. Since heating groups for radiators need a higher temp then those of ahu's the need arises to get the cooler then the supply temp, hence the mixing valve!

    Hope this explains it for you!

Similar Threads

  1. Carbon Dioxide Refrigeration
    By Andy in forum CO2
    Replies: 101
    Last Post: 12-08-2008, 03:33 AM
  2. FRICK TDSH 233 Slide Valve and guide damaged
    By 404cab in forum Industrial Compressors
    Replies: 9
    Last Post: 30-07-2008, 11:24 PM
  3. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 12:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •