    Cool Wet bulb temperature calculation



    I appreciate if any one can help me to inform me any easy formula for calculating the wet bulb temperature from air drybulb and humidity.



  2. #2
    Join Date
    Mar 2007
    Location
    India
    Age
    51
    Posts
    39
    Rep Power
    0

    Re: Wet bulb temperature calculation

    Perpetual motion, alchemy, snake oil and easy method for calculating WBT (when DBT and RH are known), all belong to same category

    I am a bit dramatic but the simplest calculation requires to compute 4 other parameters and 2 implicit equations (in simple terms, you should do a trial and error calculation or use iteration techique).

    Refer to ASHRAE Handbook of Fundamentals.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Wet bulb temperature calculation

    Use a physcometric chart.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Nov 2007
    Location
    Argentina
    Age
    71
    Posts
    12
    Rep Power
    0

    Re: Wet bulb temperature calculation

    Excuse me, may be I didnīt understand you, but if you already know the humidity and the dry bulb temp, is just a matter of looking at the chart.

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,016
    Rep Power
    19

    Re: Wet bulb temperature calculation

    Since you are knowing the Dry Bulb Temperature and the Humidity, then the best way to know the Wet Bulb temperature is to use the psycometric Chart.

  6. #6
    Join Date
    Nov 2007
    Location
    Dubai
    Age
    52
    Posts
    12
    Rep Power
    0

    Re: Wet bulb temperature calculation

    Use a physcometric chart.

  7. #7
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    621
    Rep Power
    21

    Re: Wet bulb temperature calculation

    Just in case, here's one!
    Attached Files Attached Files

  8. #8
    Join Date
    Oct 2006
    Location
    CORDOBA -ARGENTINA
    Age
    75
    Posts
    69
    Rep Power
    18

    Re: Wet bulb temperature calculation

    Despite all the valuable opinions, the tables where made by formulas , also a lot of software use such formulas.
    Of course it is easy to use the tables.

  9. #9
    Join Date
    Aug 2007
    Location
    Cyprus / Iraq
    Age
    52
    Posts
    9
    Rep Power
    0

    Re: Wet bulb temperature calculation

    is this for real????

Similar Threads

  1. bubble temperature?
    By marc5180 in forum Fundamentals
    Replies: 5
    Last Post: 21-08-2007, 02:05 PM
  2. re ref. circuit
    By shsalameh in forum Fundamentals
    Replies: 5
    Last Post: 06-08-2007, 12:59 PM
  3. Q=? h1=? mechanical schematics
    By fridg in forum Technical Speculations
    Replies: 22
    Last Post: 19-03-2006, 02:43 PM
  4. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM
  5. Replies: 5
    Last Post: 16-10-2002, 12:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •