04-11-2007, 12:01 PM #1
Intermitent Daikin Fault Code?
Hi Guys,
I have a R410A VRV system running 10 convertible units.
It's thrown up a E0 code on the controller which is an 'Outdoor activation of outdoor safety device'.
Someone else has been here before and couldn't find anything amiss and after a power down and re-enrgisation all has ben well for a few weeks.
Any pointers before I show my face next week as I'm not au-fait with Dakin kit really?
-
04-11-2007, 12:15 PM #2
Re: Intermitent Daikin Fault Code?
heres a link from another thread with some download info that should help (thankx peter)
http://www.refrigeration-engineer.co...ghlight=daikin
this fault has been covered alot on here so doing a search on here should help you
http://www.refrigeration-engineer.co...ghlight=Daikin
http://www.refrigeration-engineer.co...ghlight=Daikin
http://www.refrigeration-engineer.co...ghlight=Daikin
but from memory
E0: things to look for
LP switch
HP switch
compressor thermal cut out
condenser fan thermal cut out (had this alot)
iam sure theres more but ive only had one cup of coffee
anybody else think of any?Last edited by superswill; 04-11-2007 at 12:24 PM.
Paul
"KEEP IT COOL"
-
04-11-2007, 01:14 PM #3
Re: Intermitent Daikin Fault Code?
Looks like the Fan motor maybe the most likely culprit it seems?
-
04-11-2007, 01:22 PM #4
Re: Intermitent Daikin Fault Code?
hi, i had this problem on an r22 system..put all units in to full cooling and check operation of all components ,fans ,compressor, and gas charge...its hard to determine charge on vrv but what i noticed was my liquid line was sweating which is not meant to be you should get a warm liquid....found the system short of charge and was tripping on eo every few hours...
rgrds phil
-
04-11-2007, 01:27 PM #5
Re: Intermitent Daikin Fault Code?
Last edited by superswill; 04-11-2007 at 01:49 PM.
Paul
"KEEP IT COOL"
-
10-11-2007, 08:40 PM #6
Re: Intermitent Daikin Fault Code?
Went to site on Friday and there was no trace of a fault on the display and all seemed well!
-
11-11-2007, 11:28 PM #7
-
23-11-2007, 12:39 AM #8
Re: Intermitent Daikin Fault Code?
Came across this recently and after numerous resets, change of main pcb and further call outs i ordered the two sensors connected to measure the suction temp ( I think it was xn15 & xn16 from memory ) I did this because when I was checking the resistances I noticed that they fluctuated when I had the leads connected. I did this 3 weeks ago and have had no problems since. This was also on a 410a system. Incidentally on some 407c Daikin systems ther has been a problem with French condensor fans fitted and this threw up the same problem.
-
23-11-2007, 09:19 PM #9
Re: Intermitent Daikin Fault Code?
Cheers Vin for that.
Touch wood the systems ran OK for a couple of weeks without error so I'm keeping my head down and my fingers crossed!
Them condesors are a long way up!
-
24-11-2007, 12:37 AM #10
Re: Intermitent Daikin Fault Code?
-
24-11-2007, 12:40 AM #11
Similar Threads
-
Daikin fault codes
By Markie in forum Air ConditioningReplies: 16Last Post: 13-01-2009, 01:58 AM -
Daikin fault code E6
By casino in forum Air ConditioningReplies: 4Last Post: 24-11-2007, 12:35 PM -
mitsubishi city multi fault code
By robin r33 gtr in forum Air ConditioningReplies: 5Last Post: 05-11-2007, 10:23 PM -
UA Daikin Fault Code
By jedi in forum Air ConditioningReplies: 2Last Post: 23-07-2007, 01:44 PM -
Daikin FUYP71BV1 fault code
By Andy W in forum Air ConditioningReplies: 6Last Post: 15-02-2007, 09:11 PM