    Hi Guys,

    I have a R410A VRV system running 10 convertible units.

    It's thrown up a E0 code on the controller which is an 'Outdoor activation of outdoor safety device'.

    Someone else has been here before and couldn't find anything amiss and after a power down and re-enrgisation all has ben well for a few weeks.

    Any pointers before I show my face next week as I'm not au-fait with Dakin kit really?



  2. #2
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Intermitent Daikin Fault Code?

    heres a link from another thread with some download info that should help (thankx peter)

    http://www.refrigeration-engineer.co...ghlight=daikin

    this fault has been covered alot on here so doing a search on here should help you

    http://www.refrigeration-engineer.co...ghlight=Daikin

    http://www.refrigeration-engineer.co...ghlight=Daikin

    http://www.refrigeration-engineer.co...ghlight=Daikin

    but from memory

    E0: things to look for

    LP switch
    HP switch
    compressor thermal cut out
    condenser fan thermal cut out (had this alot)

    iam sure theres more but ive only had one cup of coffee
    anybody else think of any?
    Last edited by superswill; 04-11-2007 at 12:24 PM.
    Paul


    "KEEP IT COOL"

  3. #3
    Join Date
    Nov 2006
    Location
    Cheshire, UK
    Age
    56
    Posts
    360
    Rep Power
    18

    Re: Intermitent Daikin Fault Code?

    Looks like the Fan motor maybe the most likely culprit it seems?

  4. #4
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: Intermitent Daikin Fault Code?

    hi, i had this problem on an r22 system..put all units in to full cooling and check operation of all components ,fans ,compressor, and gas charge...its hard to determine charge on vrv but what i noticed was my liquid line was sweating which is not meant to be you should get a warm liquid....found the system short of charge and was tripping on eo every few hours...
    rgrds phil

  5. #5
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Intermitent Daikin Fault Code?

    Quote Originally Posted by sinewave View Post
    Looks like the Fan motor maybe the most likely culprit it seems?

    if the motor was faulty ie didnt run i would expect a HP fault (E7 i think) but the E0 fault just refers to outdoor "safty" not a specific component so id check the above first
    Last edited by superswill; 04-11-2007 at 01:49 PM.
    Paul


    "KEEP IT COOL"

  6. #6
    Join Date
    Nov 2006
    Location
    Cheshire, UK
    Age
    56
    Posts
    360
    Rep Power
    18

    Re: Intermitent Daikin Fault Code?

    Went to site on Friday and there was no trace of a fault on the display and all seemed well!

  7. #7
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Intermitent Daikin Fault Code?

    Quote Originally Posted by sinewave View Post
    Went to site on Friday and there was no trace of a fault on the display and all seemed well!
    loose connection?
    Paul


    "KEEP IT COOL"

  8. #8
    Join Date
    Nov 2007
    Location
    Scotland
    Age
    67
    Posts
    141
    Rep Power
    17

    Re: Intermitent Daikin Fault Code?

    Came across this recently and after numerous resets, change of main pcb and further call outs i ordered the two sensors connected to measure the suction temp ( I think it was xn15 & xn16 from memory ) I did this because when I was checking the resistances I noticed that they fluctuated when I had the leads connected. I did this 3 weeks ago and have had no problems since. This was also on a 410a system. Incidentally on some 407c Daikin systems ther has been a problem with French condensor fans fitted and this threw up the same problem.

  9. #9
    Join Date
    Nov 2006
    Location
    Cheshire, UK
    Age
    56
    Posts
    360
    Rep Power
    18

    Re: Intermitent Daikin Fault Code?

    Cheers Vin for that.


    Touch wood the systems ran OK for a couple of weeks without error so I'm keeping my head down and my fingers crossed!


    Them condesors are a long way up!

  10. #10
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Intermitent Daikin Fault Code?

    Hey Buddy i would start with checking the compressor motor overloads and fan motor overloads, if the system is not running just check the inputs to the outdoor control pcb.
    Do you know the model number?
    i will have a solution for you..

    Quote Originally Posted by sinewave View Post
    Hi Guys,

    I have a R410A VRV system running 10 convertible units.

    It's thrown up a E0 code on the controller which is an 'Outdoor activation of outdoor safety device'.

    Someone else has been here before and couldn't find anything amiss and after a power down and re-enrgisation all has ben well for a few weeks.

    Any pointers before I show my face next week as I'm not au-fait with Dakin kit really?

  11. #11
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Intermitent Daikin Fault Code?

    nah not likely..

    Quote Originally Posted by superswill View Post
    if the motor was faulty ie didnt run i would expect a HP fault (E7 i think) but the E0 fault just refers to outdoor "safty" not a specific component so id check the above first

Similar Threads

  1. Daikin fault codes
    By Markie in forum Air Conditioning
    Replies: 16
    Last Post: 13-01-2009, 01:58 AM
  2. Daikin fault code E6
    By casino in forum Air Conditioning
    Replies: 4
    Last Post: 24-11-2007, 12:35 PM
  3. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 5
    Last Post: 05-11-2007, 10:23 PM
  4. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM
  5. Daikin FUYP71BV1 fault code
    By Andy W in forum Air Conditioning
    Replies: 6
    Last Post: 15-02-2007, 09:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •