    Question start refrigerating machine



    Situation:
    I have two refrigerating circuits (R-22) in common evaporator.
    Temperature of boiling -28C (-18.4F). The leading compressor at first
    is ON. OK.
    Through 15-20 min. the catching up compressor is ON.
    After that the icing on the filter,suction line is formed,
    There are attributes of a damp course.
    Through 20-25 min. the refrigerating machine is stabilized.
    Question to the connoisseurs - It is normal whether or not?
    (I hope you me have understood)



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi, QQQ
    you english is much better than my Russian, but still lacking something
    -28 deg C evaporation, maybe -20 deg C at the compressor, you will have quite a bit of ice on the compressor, this doesnot mean wet compression. Measure the temp and pressure at the compressor inlet, same temp for pressure or within 2 deg C and you have wet compression.
    Regards. Andy

  3. #3
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    As Andy notes, superheat readings would confirm if you are having floodback programs, but your system may well be operating normally.
    Prof Sporlan

  4. #4
    Join Date
    Jan 2003
    Location
    Russia
    Posts
    10
    Rep Power
    0

    Post

    Thank all for the answers!
    More correctly to tell, that two independent circuits(two vertical
    screw compressors) have two evaporators everyone, and work on common water cooler. Is absolutely correctly noticed that on an output evaporator T=-18C. Further refrigerant flows through
    liquid suction heat exchanger and temperature rises up to 2-10C on an input of the compressor.

Similar Threads

  1. Manitowoc Ice machine taking too long to harvest..
    By nyTroX in forum Trouble Shooting
    Replies: 26
    Last Post: 08-05-2011, 09:39 PM
  2. Capacitor Start Motor
    By bryan2392 in forum Electrical
    Replies: 7
    Last Post: 27-01-2006, 07:17 PM
  3. Elderly Ice cream machine.
    By Onthecut in forum Trouble Shooting
    Replies: 12
    Last Post: 20-11-2005, 11:31 AM
  4. Cattabriga Ice Cream Machine
    By Abe in forum Trouble Shooting
    Replies: 9
    Last Post: 26-04-2003, 01:06 PM
  5. Soft Serve machine won't shut off
    By terrygoodrich in forum Commercial
    Replies: 5
    Last Post: 14-10-2001, 01:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •