    Question Mcquay water source heat pump



    I have very little experience trouble shooting refrigerant flow problems on heat pumps. So let me give you guys a crack at it.
    After evacuating and recharging unit, start up unit(10 min run time):
    suction press:65#
    head press 248#
    suc temp @ inlet of water heat exchanger 46F
    suc temp @ outlet of water heat exchanger 75F
    suc temp @ comp ahead of reversing valve 77F
    discharge line temp ahead of reversing valve 175F
    discharge line temp downsteam of rev valve 175F
    water temp inlet 80F
    water temp outlet 75F
    Seems to me suction superheat is high, discharge air temp is 90F, also seems low.
    Return air @ 65-70" (*store is in very negative pressure).
    This is the 2nd stage compressor in a 2 stage unit.
    1st stage is inoperable, blockage in refrigerant circuit.
    Got 2nd stage going to provide some heat to space and
    will have to return to repair first stage.
    Thanks
    Bernie
    M# HWH-CCH120CMFS
    S# 7 7L0809110



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60
    Without getting into your figures too deeply to start with My first thoughts are that the air temperature may not be too bad; bear in mind that if it is a 2 stage unit then performance will drop off with only one stage running.

    I always try and charge and check superheat in the cooling mode although I appreciate that may be difficult at this time of year.

    With smaller heat pumps I have often found the superheat at the compressor inlet somewhat higher than I would like but when in cooling things get back to normal.

    Sounds like you've had, and are having, fun on this one
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2001
    Location
    Chicago Il
    Age
    52
    Posts
    99
    Rep Power
    23
    Thats where I went wrong. I tried to adjust charge and superheat during heat mode.
    When I returned to the site the other day, I turned the stat to cool and dialed the charge in.
    As long as the cooling superheat is in order, I dont really care
    about the heat mode superheat.
    Its blowing warm, I'm off to the next adventure.
    Thanks
    Bernie

Similar Threads

  1. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  2. Evaporator Design-Air Source Heat Pump for water heating
    By anup in forum Technical Discussions
    Replies: 7
    Last Post: 20-03-2006, 02:26 PM
  3. water source heat pump
    By Lc_shi in forum New Technologies
    Replies: 12
    Last Post: 29-03-2005, 09:09 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. Water Source Heat Pump
    By aliugur in forum Fundamentals
    Replies: 1
    Last Post: 02-06-2002, 03:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •