    Difference between NTC. PT 100 & thermocouples



    We have seen various types of probes being used for temp sensing. What is the basic difference & what applications is suited best for each of these?



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Difference between NTC. PT 100 & thermocouples

    Hi smpsmp45
    NTC means Negative Temperature Coefficient = when the temp rises the resistance drops - common for thermister type sensors used in BMS in Ausi.
    PT 100 = Platinum RTD (Resistance Temperature Detector) used for a temp range of 0C to 100C. These sensors are reliable, linnier and have optimal characteristics over a wide range. They have a PTC (Positive Temp Coefficient). material = noble.
    Thermocouples are basicly two dissimilar mettals where at the junction (join) of the metals (wire) a voltage is created which changes with temp. These sensors are used for accuracy at mainly high temps up to about 2500C.
    To summarise - sensor types
    Thermister = room temp, water temp
    RTD = room temp, water temp
    Thermocouple = high temp
    -characteristics
    NTC
    PTC

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Difference between NTC. PT 100 & thermocouples

    An not to to forget, the resistance of a PT100 = 100 ohm at 0°C.

    You also have PT1000 (1000 ohms at 0°C)
    They made a PT1000 because it's less prone to cable resistance.
    Many PT100 or PT1000's have 3 wires to calculate the resistance of the wires between probe and display to compensate this difference automatically.

    Thermocouple use also if you need a fast response of the temperature.

    If you need accuracy at 0.1°C, use PT100 or PT1000 (=expensive), otherwise PTC and NTC is the sensor for almost any HVAC/R application (=cheap)
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Difference between NTC. PT 100 & thermocouples

    That is very good response. Many thanks

  5. #5
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: Difference between NTC. PT 100 & thermocouples

    [quote=Peter_1;82494]An not to to forget, the resistance of a PT100 = 100 ohm at 0°C.

    You also have PT1000 (1000 ohms at 0°C)
    quote]

    Are you sure of it?
    I guess 1000 ohms at 25C...

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Difference between NTC. PT 100 & thermocouples

    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Difference between NTC. PT 100 & thermocouples

    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: Difference between NTC. PT 100 & thermocouples

    OK!
    But I told about PTC and NTC thermistors.The rated resistance Rr is the resistance value at temperature Tr that is 25C, unless otherwise specified. In the refrigeration field we often have NTC thermistors with 10kOhm at 25C and PTC thermistors with 1kOhm at 25C
    Regards!

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Difference between NTC. PT 100 & thermocouples

    So, I was sure.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Difference between NTC. PT 100 & thermocouples

    I also came to know that With PT 100, the only error which can take place is sensor cable broken. But with Thermocouples one can land is big problems if they go faulty. The control mechanism with thermocoules may not work & can make the compressor run all the time.

Similar Threads

  1. Difference between geo thermal and air to air
    By ianybeany in forum Heat Pumps
    Replies: 5
    Last Post: 23-02-2008, 11:15 PM
  2. Replies: 4
    Last Post: 10-06-2005, 12:25 AM
  3. temperature difference of evaporator coil
    By dantoubiana in forum Trouble Shooting
    Replies: 12
    Last Post: 03-05-2003, 03:46 AM
  4. Difference
    By Abe in forum Commercial
    Replies: 11
    Last Post: 03-04-2003, 03:34 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •