    Difference between NTC. PT 100 & thermocouples
    We have seen various types of probes being used for temp sensing. What is the basic difference & what applications is suited best for each of these?
    Aug 2007
    Sydney
    52
    1,083
    Re: Difference between NTC. PT 100 & thermocouples
    Hi smpsmp45
    NTC means Negative Temperature Coefficient = when the temp rises the resistance drops - common for thermister type sensors used in BMS in Ausi.
    PT 100 = Platinum RTD (Resistance Temperature Detector) used for a temp range of 0C to 100C. These sensors are reliable, linnier and have optimal characteristics over a wide range. They have a PTC (Positive Temp Coefficient). material = noble.
    Thermocouples are basicly two dissimilar mettals where at the junction (join) of the metals (wire) a voltage is created which changes with temp. These sensors are used for accuracy at mainly high temps up to about 2500C.
    To summarise - sensor types
    Thermister = room temp, water temp
    RTD = room temp, water temp
    Thermocouple = high temp
    -characteristics
    NTC
    PTC
    Oct 2003
    5,630
    An not to to forget, the resistance of a PT100 = 100 ohm at 0°C.
    You also have PT1000 (1000 ohms at 0°C)
    They made a PT1000 because it's less prone to cable resistance.
    Many PT100 or PT1000's have 3 wires to calculate the resistance of the wires between probe and display to compensate this difference automatically.
    Thermocouple use also if you need a fast response of the temperature.
    If you need accuracy at 0.1°C, use PT100 or PT1000 (=expensive), otherwise PTC and NTC is the sensor for almost any HVAC/R application (=cheap)
    India
    688
    That is very good response. Many thanks
    Aug 2007
    Russia
    138
    [quote=Peter_1;82494]An not to to forget, the resistance of a PT100 = 100 ohm at 0°C.
    quote]
    Are you sure of it?
    I guess 1000 ohms at 25C...
    Oct 2003
    5,630
    Oct 2003
    5,630
    Aug 2007
    Russia
    138
    OK!
    But I told about PTC and NTC thermistors.The rated resistance Rr is the resistance value at temperature Tr that is 25C, unless otherwise specified. In the refrigeration field we often have NTC thermistors with 10kOhm at 25C and PTC thermistors with 1kOhm at 25C
    Regards!
    Oct 2003
    5,630
    So, I was sure.
    India
    688
    I also came to know that With PT 100, the only error which can take place is sensor cable broken. But with Thermocouples one can land is big problems if they go faulty. The control mechanism with thermocoules may not work & can make the compressor run all the time.
  1. Difference between geo thermal and air to air
    By ianybeany in forum Heat Pumps
    Last Post: 23-02-2008, 11:15 PM
  2. Replies: 4
    Last Post: 10-06-2005, 12:25 AM
  3. temperature difference of evaporator coil
    By dantoubiana in forum Trouble Shooting
    Last Post: 03-05-2003, 03:46 AM
  4. Difference
    By Abe in forum Commercial
    Last Post: 03-04-2003, 03:34 AM