    Slow oil return - Carrier 5H86 compressor



    Currently there some problems with the oil returing back to the compressor (oil level just below slightglass). The chilled water return temp to chiller was 11degC and the suction pressure was at 2bar. TEV superheat was set at 8degC. At times the net oil pressure goes below the 2.5bar recommended. if this were to persist, the unloaders will not be able to load due to lack of hydraulic pressure from the oil. The temperature controller (Honeywell) was set with a desired temp from 9 to 12deg with 1deg differential. Ambient temp varies from 32deg in the day and 20deg at night. AHU coils were also chemically cleaned with temp diff across coil within 2 to 5deg but the air flow rate wasn't checked yet.

    One of the compressors was recently top overhauled and found the piston crowns with dented markings and the suction valve plates broken. What's the likely caused? I'm under the notion of an oil slugging or floodbacks due to sudden load increments. But here again the distance from the chiller unit (below the compressor suction head) is about 1m. Another finding is that the TEV bulb is place on the vertical pipe before the suction not at 4 or 8 o'clock on the horizontal pipe.



  2. #2
    Join Date
    Nov 2007
    Location
    Australia
    Age
    70
    Posts
    10
    Rep Power
    0

    Re: Slow oil return - Carrier 5H86 compressor

    mike

    Much more detail and data would be required to make any sort of informed recommendation, but it sounds like liquid refrigerant at the compressor, possibly caused by low water flow through the chiller....it could be as simple as sludge build up in the oil return float outlet orifice reducing the rate of return oil, or faulty crankcase heater, allowing liquid refrigerant to condense in the oil during shut down periods, especially during cool nights. TD across the AHU coils seems minimum, which could also indicate low chilled water flow. Broken suction valves is also an indication of possible liquid refrigerant flooding or oil slugging, among other things. Is this a factory built chiller, or made up on site. Is the chiller a small set with the one Carrier comp, or is the chiller large with multiple compressors, and if so are the other compressors having the same problem. Hope this assists in some way and I would be very interested in following the rectifications.

    Good Luck.

  3. #3
    Join Date
    Oct 2007
    Location
    Belgium
    Posts
    11
    Rep Power
    0

    Re: Slow oil return - Carrier 5H86 compressor

    Hey Mike,

    It sounds like you already found your problem.
    The compressor did suffer causes like slugging/floodback.

    And you are also right that the TEV bulb isn't mounted right.
    It has to be mounted horizontally, and then depending on the size of your suction conduit you place it accordingly.
    DIAM 10 --> at 1 o'clock
    DIAM 20 --> between 2 and 3 o'clock
    DIAM 30 --> between 3 and 4 o'clock
    everything above DIAM 30 you place at 4 o'clock.

    This should help with your OIL problem as well.
    Because of the refrigerant fluid that causes floodstarts.
    Also check if your crankcase heater is still functioning right. Not to HOT and not to COLD.

    Ben

  4. #4
    Join Date
    Feb 2007
    Location
    Australia
    Age
    70
    Posts
    15
    Rep Power
    0

    Re: Slow oil return - Carrier 5H86 compressor

    Mike,

    Ensure that the compressor pumps down correctly when the water reaches set point and the solenoid valve is not leaking otherwise liquid refrigerant could return to compressor. Should suction pressure rise quickly after pump down when the solenoid valve seats correctly, the valve plates probably have failed.
    If the compressor is noisy, damage may already occured. I'm assuming that one compressor per refrigerant circuit.

    Gary

  5. #5
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    85
    Rep Power
    17

    Re: Slow oil return - Carrier 5H86 compressor

    Is the tx valve bulb well insulated , this sounds like a low water flow or load problem , Have you tried controlling the leaving water temp instead of return?

Similar Threads

  1. carrier 30gx compressor wiring question
    By knight rider in forum Technical Discussions
    Replies: 8
    Last Post: 12-07-2009, 01:40 PM
  2. 30GX Carrier screw compressor
    By malik55 in forum Air Conditioning
    Replies: 9
    Last Post: 19-04-2009, 12:16 PM
  3. Carrier Compressor
    By AAP in forum Air Conditioning
    Replies: 7
    Last Post: 02-05-2008, 06:46 PM
  4. Looking for Carrier Compressor
    By AAP in forum Chit Chat & Service Stories
    Replies: 1
    Last Post: 19-07-2007, 11:21 AM
  5. carrier 5h compressor
    By altaf22m in forum Air Conditioning
    Replies: 0
    Last Post: 04-08-2005, 12:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •