    Iam new to refrigeration. What happens if Filter Drier gets moisture content. How can we check filter drier moisture content. does moisture in filter drier show any direct effect on compressor.
    thankyou
    caster
    Feb 2007
    2,473
    45
    Re: Filter Drier Moisture content
    Welcome.
    First, the drier is meant to catch moisture so as long as it doesn't get "filled" with more moisture than it can hold/store then it's not an issue.
    (Well, apart from the fact that there shouldn't be moisture in the system in the first place, it's a good indication of poor workmanship)
    The easiest way to see if you got moisture in the system is by fitting a sight glass with moisture indicator.
    (There are other ways but the sight glass is easy and cheap)
    And YES, it will damage the compressor. For example, modern refrigeration compressor oils will become acidic even with small amounts of moisture in them.
    Feb 2006
    derbyshire
    610
    one of the first things that it will effect but not the only is the expansion valve or metering unit will start blocking and shuting the system down on LP,also the drier may run cold to the touch on the out going side,you can also check this with a infa red thermometer for ease, theese are just basic pointers for you that will arise normaly before any problems occur with the compressor, an oil change is a must on a contaminated system,this will help protect it while changing the drier at least once should remove the problem unless its saturated,now thats another storey.
    caster's Avatar
    caster Guest
    Thanks for the information guys.
    Oct 2003
    5,630
    34
    Filter can hold more mositure with cold liquid (like in winter) and release it back when liquid becomes warm (summer) and therefore blocking your TEV
  1. 2-stage cascade
    By before in forum CPU Overclockers
    Last Post: 20-12-2008, 10:06 PM
  2. How is a filter drier sized
    By kengineering in forum Technical Discussions
    Last Post: 08-08-2006, 05:00 AM
  3. DW Copeland
    By Abe in forum Trouble Shooting
    Last Post: 19-11-2002, 02:54 PM
  4. Shelf life of an uncapped dessicant drier.
    By eberg in forum Air Conditioning
    Last Post: 22-08-2001, 01:22 PM
  5. Drier Position
    By subzero*psia in forum Commercial
    Last Post: 23-07-2001, 10:28 PM