    Danfoss TXV with MOP



    I have a problem in three cases and one frezzer island:
    I instaled TXV with MOP in my cases and island but when reach the MOP point close and stay close. If I change those valves for sporland it will be ok., but I want to find out how to handle those?.
    I am in Dominican Republic (Caribbean Area). Thanks



  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Danfoss TXV with MOP

    Hi there,

    The TEV head must be little bit warmer than the bulb, otherwise the valve will close. Somehow you have to create this temperature difference. I had the same problem once and I solved it by wrapping the head with heating element (of course very little wattage).

    Hope this helps.

    cheers
    Even Einstein Asked Questions

  3. #3
    Join Date
    Mar 2007
    Location
    south africa
    Age
    55
    Posts
    14
    Rep Power
    0

    Re: Danfoss TXV with MOP

    Hey Chap!

    A Tev With A Mop(maximum Operation Pressure)is Specifically Installed In Island Freezers And Freezer Installations So That After Defrosts And Other High Load Conditions The Compressor Does Not Overload.keeps The Suction Pressure At A Max.when The Max Is Reached The Valve Closes Off.same As Cpr (crankcase Pressure Regulator).
    If You Install A Normal Low Temp Valve With No Means Of Throttling The Suction And Dont Have A Cpr.good Chance The Compressor Will Overload After Defrost Or When Cabinet Is Warm And Probably Cook.

  4. #4
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: Danfoss TXV with MOP

    If it shuts off at hi suction pressures and stays shut (with hi pressure still) then this is how it works, drop the suction pressure and it will open up again. If it shuts off at hi suction pressures but will not open back up once suction drops below MOP rating then you have a problem.
    ...and she said "give it to me you big fridgie"

  5. #5
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Danfoss TXV with MOP

    I heard a whisper about a certain batch of valves.

  6. #6
    Join Date
    Nov 2007
    Location
    Australia
    Age
    70
    Posts
    10
    Rep Power
    0

    Re: Danfoss TXV with MOP

    I heard the same whispers MarkFiddy. But as 750 valve remarks, if the valve remains closed at low suction below MOP, then it will be a faulty TXV. Replace the valve.

  7. #7
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    85
    Rep Power
    17

    Re: Danfoss TXV with MOP

    Quote Originally Posted by MarkFiddy View Post
    I heard a whisper about a certain batch of valves.
    Not unheard of ,a MOP valve is made by undercharging the power element and are easy for the factory to make a mistake , I had a sporlan like that I took it back to the supplier who said it wont bed the head , I got him to pull 2 more off the shelf put all 3 bulbs in a glass of cold water then used a straight edge and calipers to measure the diaphram distance , sure enough the one he gave me was a few milimeters short giving the high super heat

  8. #8
    Join Date
    Nov 2007
    Location
    USA
    Posts
    9
    Rep Power
    0

    Re: Danfoss TXV with MOP

    One suggestion is to call Danfoss technical support and have pressure readings and such on hand for them to assist in the problem solution. Otherwise stick with what works.

  9. #9
    Join Date
    Nov 2007
    Location
    Canada
    Posts
    5
    Rep Power
    0

    Re: Danfoss TXV with MOP

    HI
    Often MOP with Danfoss might work erracticly since the head is maintained colder because closer outlet(evaporator) connection. With Sporlan, the inlet (higher liquid temperature) will often maintain the head at a higher temperature.

Similar Threads

  1. Oil cooling circuit on Danfoss compressors?
    By The MG Pony in forum Fundamentals
    Replies: 15
    Last Post: 16-10-2010, 12:33 PM
  2. Danfoss remote control
    By spr2003 in forum Electrical
    Replies: 3
    Last Post: 27-04-2007, 09:49 AM
  3. Danfoss Compressors
    By iceman007 in forum Fundamentals
    Replies: 0
    Last Post: 28-07-2006, 06:32 PM
  4. Danfoss compressor
    By wincanton1 in forum Commercial
    Replies: 4
    Last Post: 04-07-2006, 10:50 AM
  5. Danfoss parellel scroll compressors
    By Lc_shi in forum Technical Discussions
    Replies: 2
    Last Post: 30-03-2006, 08:20 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •