Thread: dehumidification
30-10-2007, 09:21 AM #1
dehumidification
Hi All
At what evaporating temperature would you remove the maximum amount of water from at a air temperature of 25 deg C and 40 deg C
Hope it makes senses
CB
30-10-2007, 08:59 PM #2
Re: dehumidification
What is the expected wet bulb temperature at those dry bulbs?
31-10-2007, 01:36 AM #3
+1 degree celcius. An evaporating temperature below this will cause condensation to freeze on the coil which decreases efficiency. A good coil will enable you to achieve an air dew point of 6 - 7 deg C
01-11-2007, 10:37 AM #4
Correct, as Brain_UK mantioned what is the wet bulb temperature. This depends on the web bulb and dry bulb temperature.