    Daikin VRV electrical wiring

    I have been asked to quote on wiring five Daikin VRV systems each with 7 to 8 indoor units 18-20Kw cooling each. Though I have been working on Daikin for quite a while this is my first VRV system. What I would like to know is, does the electrical feed for each of the indoor fans have to go back to the outdoor unit or is there another way to wire them?

  2. #2
    Join Date
    Aug 2005
    Location
    uk
    Age
    45
    Posts
    82
    Rep Power
    19

    Re: Daikin VRV electrical wiring

    Quote Originally Posted by anracau View Post
    I have been asked to quote on wiring five Daikin VRV systems each with 7 to 8 indoor units 18-20Kw cooling each. Though I have been working on Daikin for quite a while this is my first VRV system. What I would like to know is, does the electrical feed for each of the indoor fans have to go back to the outdoor unit or is there another way to wire them?
    each unit has a power supply
    then the units are daisy chained to each other including the bs box aswell. linking then back to the condenser

  3. #3
    anracau's Avatar
    anracau Guest

    Re: Daikin VRV electrical wiring

    So each indoor unit has an independent power supply & only the screened interconnects go back to the oputdoor unit? What is the bs box?

  4. #4
    Join Date
    Aug 2005
    Location
    uk
    Age
    45
    Posts
    82
    Rep Power
    19

    Re: Daikin VRV electrical wiring

    Quote Originally Posted by anracau View Post
    So each indoor unit has an independent power supply & only the screened interconnects go back to the oputdoor unit? What is the bs box?
    yep that is correct, bs box is where the 3 pipes go in and only 2 come out to go to the indoor unit

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: Daikin VRV electrical wiring

    Bs boxes are located next to each indoor unit and contain a solonoid valve which opens and lets through refrigerant (to heat or cool) depending on what the indoor unit is asking for.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  6. #6
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Daikin VRV electrical wiring

    Hello Anracau,

    The wiring is quite straight forward on the VRV system, and can be broken down into power supply wiring, basic VRV control wiring (must be present on all VRV systems) and controls wiring (depends on how you want to control the VRV systems and if you have any centralised controls)

    Power Supply Wiring
    On the outdoor unit you need a 3 phase + neutral power supply. Make sure the neutral is wired permanently to the unit (i.e. not switched through the isolator). If you apply just the 3 phase without the neutral connected, the main outdoor PCB may go “BANG”. Always use a 3 pole MCB, don’t use individual fuses or MCBs.

    On the indoor units you can run a 230V AC ring main, with switch spurs to each indoor unit and BS Box if its is a heat recovery system. (3 or 5 amps depending on the size of the indoor unit). I would recommend a fused spur ( not switched spur) for the wall and floor mounted units. This is because if the end user switched off the spur to one indoor unit then the entire system will shutdown (this is a safety feature). All and floor mounted units are most accessible to the end users.

    VRV Basic Wiring
    You should get a wiring diagram for the systems you are installing from the supplier. The type of cable you need if 2 core non-screened 0.75mm² as specified by Daikin. You can help yourself by using 2 colours (white and black) for the different wiring loops. E.g. use the black cable between the outdoor units and the BS Boxes. Use the white cable between the BS Box and the indoor units. Use the black cables between the indoor units and the remote controllers. This should help to reduce any wiring errors. The simplest way to remember the basic wiring is to remember that the wiring follows exactly the field piping. All the BS Boxes physically piped to one outdoor unit must also be wired to the outdoor unit. All indoor units piped to a BS Box must be wired to that BS Box.
    There is a minimum cable separation distance between the control cables and power cables. E.g. say the power cable was consuming 10amps, the control cables if running alongside should be at least 300mm away. There is table in the installation manual.

    Control Wiring
    The type of cable is the same as above. From the centralised controls you will need to run cables to the outdoor units.
    In case you have group control, you may need to daisy chain between the remote controller and several indoor units.

    There are examples of control and power wiring in the installation manuals. Spend an hour to read the manual and you won’t have a problem.

    Regards

    Obi Wan
    Attached Images Attached Images
    Last edited by Obi Wan; 28-10-2007 at 01:29 PM. Reason: Pictures

  7. #7
    Ladymechdsgnr's Avatar
    Ladymechdsgnr Guest

    Re: Daikin VRV electrical wiring

    hi, m just browsing thru this post on VRV wiring, just wanna say that the information from this post is helpful.

  8. #8
    anracau's Avatar
    anracau Guest

    Re: Daikin VRV electrical wiring

    Thanks for the help.

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Daikin VRV electrical wiring

    The Diakin equipment supplier should supply a detailed wiring diagram as part of the quote/install package.

    Ask to have sight of it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Feb 2008
    Location
    malta europe
    Age
    50
    Posts
    5
    Rep Power
    0

    Re: Daikin VRV electrical wiring

    dear sir,
    i have a query i am new on vrv's and i have a question ,
    my client have two high wall units and wants to replace them with two casette units of the same 28.000 btu's is that possible ?( the control circuit board is the same as specified on the circuitdiagram).there is no info on the indoor units. actually on the outdoor is saying 410 a but how can i know the casette type of what refrigerant they are? in the old days you can actually see that on the diaphram of the txv but these does have the same info ?does a 410a indoor means only that refrigerant?

  11. #11
    Join Date
    Dec 2007
    Location
    London
    Age
    57
    Posts
    83
    Rep Power
    17

    Thumbs up Re: Daikin VRV electrical wiring

    Quote Originally Posted by steve bajada View Post
    dear sir,
    i have a query i am new on vrv's and i have a question ,
    my client have two high wall units and wants to replace them with two casette units of the same 28.000 btu's is that possible ?( the control circuit board is the same as specified on the circuitdiagram).there is no info on the indoor units. actually on the outdoor is saying 410 a but how can i know the casette type of what refrigerant they are? in the old days you can actually see that on the diaphram of the txv but these does have the same info ?does a 410a indoor means only that refrigerant?

    All indoor units are compatible with the outdoor unit if the system is VRV.So i don't need models to confirm it.Just change it and that's it.There should be no problem as you won't do any different kw .This is what matter to keep the system in balance.Indoor units design doesn't matter just kw.

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Daikin VRV electrical wiring

    Do you have model no. on casete units!

  13. #13
    Join Date
    Nov 2009
    Location
    england
    Age
    46
    Posts
    18
    Rep Power
    0

    Re: Daikin VRV electrical wiring

    Why cant the control cable be screened??

  14. #14
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin VRV electrical wiring

    Quote Originally Posted by SUBCONTRACTOR View Post
    All indoor units are compatible with the outdoor unit if the system is VRV.So i don't need models to confirm it.Just change it and that's it.There should be no problem as you won't do any different kw .This is what matter to keep the system in balance.Indoor units design doesn't matter just kw.
    Quote Originally Posted by anracau View Post
    I have been asked to quote on wiring five Daikin VRV systems each with 7 to 8 indoor units 18-20Kw cooling each. Though I have been working on Daikin for quite a while this is my first VRV system. What I would like to know is, does the electrical feed for each of the indoor fans have to go back to the outdoor unit or is there another way to wire them?
    Only 410a vrv indoor units can be conected to a 410a vrv out door unit this is easily identified by the outdoor/indoor model numbers

    Outdoor example REYQ10P8Y1
    R = Outdoor unit

    EY= Heat Recovery (3 pipe) / XY= Heat Pump (2 pipe) / X Cooling only (2 pipe)

    Q = 410A (refrigerant type)

    10 = Capacity in horse power (1 hp = a capacity index of 25)

    P7/8 = Series of unit (VRV III) / M7/8 = VRVII

    Y1 = 3 phase 415v

    Indoor example FXSQ50PV1

    FX = IVRV ndoor unit
    S = Ducted indoor / A = Wall Mount / ......
    Q = 410A (refrigerant type)
    P = Series of unit
    V1 = Single phase 230v

Similar Threads

  1. Daikin vrv control wiring
    By Jase in forum Air Conditioning
    Replies: 4
    Last Post: 23-03-2011, 05:01 AM
  2. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 10:01 AM
  3. Transmission wiring on Daikin VRV2
    By Markie in forum Air Conditioning
    Replies: 19
    Last Post: 25-09-2009, 06:24 PM
  4. part p
    By eggs in forum Electrical
    Replies: 25
    Last Post: 15-11-2007, 09:55 PM
  5. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •