    TXV hunting in a walkin cooler



    I've an R22 walk in cooler that's not keeping temps real well. Target temp is 34°F or 1°C. This cooler has NO history of ever running correctly. The cooler will recover well to it's best temp even when subject to a sudden and heavy heat load, but never does fully come down to temp.

    I've verified the thermostat is set and working correctly. Pressures look good for R22 medium temp, sight glass is clear but I'm seeing excessive hunting on the expansion valve, from 1°K to 10°K.

    A quick inventory of the cooler shows a 26.6kBtu/h evaporator, a 28.5kBtu/h condensing unit and a 18kBtu/h expansion valve.

    I'd have expected an over sized valve to have hunting problems, but this valve appears to be undersized for the application.

    First thought had been to simply replace the thermal element, but I'm leaning towards replacing the whole valve.

    Have I missed something obvious or does it look like I'm on the correct path?

    Thanks!



  2. #2
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: TXV hunting in a walkin cooler

    Try repositioning the TXV phial on the suction pipe @ the cooler.

    Regards
    Jase

  3. #3
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: TXV hunting in a walkin cooler

    Hi dkemper
    What are the operating pressures?
    If the valve is too small and the evap has been starving for a long time the evap could be oil logged as this system is on R22.
    Has the compressor had oil added regularly?
    Probably would be best to replace the valve with the correct size and the watch the oil level in the compressor, if the evap is oil logged.
    Let us know how you go.
    Paul

  4. #4
    Join Date
    Oct 2007
    Location
    Not Sure?
    Posts
    76
    Rep Power
    17

    Re: TXV hunting in a walkin cooler

    Still no response????

  5. #5
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: TXV hunting in a walkin cooler

    What is the measured superheat? If the valve is to small it will not be able to modulate properly the valve will be fully open but not letting enough liquid into the evaporator to get correct cooling. Fit the correct sized valve and you should be OK.

    Ian

  6. #6
    Join Date
    Feb 2006
    Location
    valencia
    Posts
    15
    Rep Power
    0

    Re: TXV hunting in a walkin cooler

    at +1Cº need defrost, electric or hot gas

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: TXV hunting in a walkin cooler

    What are the evaporator air in and air out temps? Insufficient airflow would reduce the heat load, which could cause the TXV to hunt. In effect, the valve would be oversized for the actual load.

    If the system has never performed correctly, we might look for something like wrong fan blades or blades installed backwards, backhanding rather than cupping the air. If the fan motors are 3 phase, they might be running backwards.

    Does the system have an EPR or SORIT valve? If so, the setting may be too high, limiting the load.
    Last edited by Gary; 14-11-2007 at 04:32 PM.

  8. #8
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: TXV hunting in a walkin cooler

    Hi, one question I would ask, is it a holding freezer or a pull down one it seems to me that its sized as holding freezer and has trouble pulling the temp down. only a thought

    Regards Toosh

  9. #9
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: TXV hunting in a walkin cooler

    Hi.

    If the the evaporator and condensing unit are correctly matched and the TEV is undersized then you must have bad heat exchange at the evaporator!! or poor airflow, or a internally coated evaporator coil, not allowing optimum heat exchange.

    CB

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: TXV hunting in a walkin cooler

    Indeed. Airflow problems can cause refrigerant flow problems, but not vice-versa.

    That's why a logical trouble shooting procedure would have us checking for and correcting any airflow problems before putting our gauges on the machine.

Similar Threads

  1. Hunting Etc.
    By subzero*psia in forum Hobbies
    Replies: 27
    Last Post: 19-09-2010, 01:40 PM
  2. NH3 thermosiphon oil cooler
    By cygbob in forum NH3
    Replies: 38
    Last Post: 22-06-2008, 05:12 PM
  3. Walkin cooler running to warm need help
    By The Butcher in forum Trouble Shooting
    Replies: 7
    Last Post: 03-08-2007, 09:19 PM
  4. Walkin cooler
    By masooda in forum Trouble Shooting
    Replies: 4
    Last Post: 09-02-2007, 04:57 PM
  5. Thermo-syphon Oil Cooler
    By B.B. in forum Industrial
    Replies: 5
    Last Post: 31-10-2005, 01:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •