    About Delta T



    Kindly suggest for my queries

    System : Cold Room
    Room Temp :0ºC

    Total Heat Load : 42 KW
    No of Evaporators : 2
    Evaporator capacity: 21 KW each
    Secondary Coolant :35% Prop.Glycol
    Glycol Inlet :-8ºC
    Glycol Outlet :-4ºC
    Flow rate :9.4 m3 /Hr. for a single unit.

    Query:

    • Here the T = 4ºC is common. Suppose I make the Inlet /outlet temp.like -10/-6ºC (OR) -1 / -5ºC what will be the result to the room temperature? How can I justify while selecting the equipment?

    • Considering 7 cold rooms to the same capacity & same parameters the number of evaporators is 14. I have to store the glycol in a tank and rechilling it thro PHE. How can I calculate the flow rate for PHE?


    Waiting for your suggestions.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: About Delta T

    You can say that your capacity will drop +/- linear with the DT.
    For me, your DT is 8K (room at 0°C and glycol entering at -8°C)
    Now, you will enter at -5°C.
    So a drop of +/- 37%
    Q= k.A.DT (k and A remains the same)

    Flow rate, is it not just 9.4/unit x 14 units?
    Evaporating at 5 to 7 K lower then the desired outlet temperature of -8°C (so -13°C to -15°C)
    You will need software to calculate this because each manufacturer can tell you what capacity you will have with a specific glycol mixture. Don't forget also that the viscosity will increase with lowering the temperature.

    You will need bigger pumps.
    Pressure drop will also increase due to the large mass flow of 14 units
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Part Wind/ Star Delta
    By reggie in forum Technical Speculations
    Replies: 34
    Last Post: 27-08-2008, 05:47 AM
  2. Understanding star delta
    By marc5180 in forum Fundamentals
    Replies: 21
    Last Post: 26-09-2007, 01:21 AM
  3. Replies: 12
    Last Post: 18-03-2007, 05:25 PM
  4. 3phase compressor.
    By Pandrone in forum Air Conditioning
    Replies: 15
    Last Post: 11-01-2005, 09:34 PM
  5. Large tonnage De-coupling
    By MANIS in forum Technical Discussions
    Replies: 14
    Last Post: 14-08-2004, 06:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •