    E4 fault on RXYQ8P7



    Hi everyone, how are you...
    Got a problem on a VRV RXYQ8P7W1B (unused), i've made the commissioning 7 days ago. The system failed to E4 the first night after ( low pressure detection by pressure sensor).
    I recovered the refrigerant and found the good amount ( total=9.53kg ).
    In the meantime i tested the pressure sensor reliability compared to my low pressure gauge manifold and the service checker data. I made a complete vaccum during 3 hours and started again to check it in heating mode.
    After the system reached the HP target (50°C), i found the discharge pressure slightly high : 112 to 115 °C with discharge step down control activation, there were ice just after the main EXV output to the heat exchanger (just at the beginning).
    The system failed to E4 again the last night !!! don't know exactly why i'm getting bored by an unused system !
    Maybe a matter of bad EXV or something like that, i got a data recording of the 2nd commissioning.
    Need your kind advises please it's for a child care centre..
    cool#9
    Last edited by cool#9; 20-10-2007 at 05:44 PM.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: E4 fault on RXYQ12P7

    You are sure about the additional charge?

    Total pipe length about 10-15 meters?

    (9.53-8.6 = ~1kg = ~8m 1/2" pipe)
    Last edited by The Viking; 19-10-2007 at 06:29 PM.

  3. #3
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: E4 fault on RXYQ12P7

    Quote Originally Posted by The Viking View Post
    You are sure about the additional charge?

    Total pipe length about 10-15 meters?

    (9.53-8.6 = ~1kg = ~8m 1/2" pipe)
    Hi Viking
    The original charge on the nameplate is 7.7 kg.
    The 1/4 length is 43m x 0.022 so 0.946 kg
    The 3/8 length is 15m x 0.059 so 0.885 kg
    Additional refrigerant is *******1.831 kg*****
    Total amount is*************9.530 kg*****

    Your remark is true we have to check the length once again maybe there's a mistake, we'll dig it on next monday morning..
    Thanx
    cool#9

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: E4 fault on RXYQ12P7

    Ok,
    Just a thought...
    But in the manual I downloaded it said 8.6kg and 1/2" to the first T.
    Hmm, can't believe that a Japanese manual would be wong.

  5. #5
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: E4 fault on RXYQ12P7

    Quote Originally Posted by The Viking View Post
    Ok,
    Just a thought...
    But in the manual I downloaded it said 8.6kg and 1/2" to the first T.
    Hmm, can't believe that a Japanese manual would be wong.
    Hi The Viking
    I made a mistake.. it's RXYQ8P7W1B !!!
    Sorry i'm editing my post.
    cool#9

  6. #6
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: E4 fault on RXYQ12P7

    Cool#9

    Can you check the actual cables coming out of the low pressure sensor? They may be broken. If that is the case you will need to replace the pressure sensor. To do this you will need to remove the entire refrigerant as the sensor is a brazed type. Don’t forget to wet-rag the sensor when brazing.

    Let us know what you find.

    Obi Wan.

  7. #7
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: E4 fault on RXYQ8P7

    Thanks Obi Wan
    It's true the cables from the low pressure sensor were tighten high...
    We had a lot of problems with HP sensors and JA fault on other VRVs, P series.
    In this case we had no JC fault but your opinion is good, we maybe have the same problem due to wrong reading.
    If the additional charge is correct upon the field length we will change both LP sensor and main EXV.
    rgds
    cool#9

  8. #8
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: E4 fault on RXYQ12P7

    I have also had the same type of problem. The low pressure sensor was changed and we have had no problems with the system.

  9. #9
    vijaypal15's Avatar
    vijaypal15 Guest

    Re: E4 fault on RXYQ8P7

    HI MATE ,THIS IS VIJAY i m a/c tech ,i just joined this site ,i read the problem which u r facing ,my suggesion is just double check the length of pipe and check weather any additional charge required cos these units r very precisely charged and my it could be pressure swich fault ,i dont think its expension valve
    cheers

  10. #10
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: E4 fault on RXYQ8P7

    Quote Originally Posted by vijaypal15 View Post
    HI MATE ,THIS IS VIJAY i m a/c tech ,i just joined this site ,i read the problem which u r facing ,my suggesion is just double check the length of pipe and check weather any additional charge required cos these units r very precisely charged and my it could be pressure swich fault ,i dont think its expension valve
    cheers
    Thanks vijaypal15 and welcome on RE forum.
    I'd like to thanks everyone also cause i'll begin the week with good advises.
    I will tell you how i'm getting on.
    rgds
    cool#9

  11. #11
    bendoky's Avatar
    bendoky Guest

    Re: E4 fault on RXYQ12P7

    Hi mate:
    as you know that E-4 is a malfunctiong code for low pressure in suction side. try the followings:

    1. pressure switch- if the refrigerant pressure side becomes abnormally low.the pressuer switch stop the operation of the unit automatically.
    2. pressure control valve- It controls the cooling operation. the low pressure valve sense the low pressure which is about 4kgf/cm-g or less (the pressure of the fan coil unit) and bypass the discharge gas from the compressor to the accumulator.

  12. #12
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: E4 fault on RXYQ12P7

    Hello All,

    Reading some of the posts, some of you are correctly relating to the E4 error to a Low pressure switch. In case of the split or Sky Air systems this is correct. However on the VRV systems there is no low pressure switch but there is a low pressure sensor. If you get an E4 on the VRV system then it can mean that the low pressure is very low (less then 0.07MPa). This can be due to refrigerant shortage, Faulty low pressure sensor, Or a faulty main outdoor PCB. The hot gas bypass valve should also be checked. (I once had the ¼” pipe totally blocked with over brazing on the hot gas bypass valve)

    The above would be the case during normal operation.

    You can also get the E4 error code during the mandatory test operation on the VRV II & III systems. In this case it can mean something different. I attach a list of error codes and there descriptions during the test operation.

    Obi Wan.
    Attached Images Attached Images
    Last edited by Obi Wan; 23-10-2007 at 09:59 PM. Reason: Ahh yes the attachment!

  13. #13
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: E4 fault on RXYQ8P7

    Hi, how are you...?
    Ok, i went back seriously on this problem on found the length were wrong...
    After new calculation i put 1.88 kg of R410A and the system didn' t fail last night, the Child Centre opened this morning , for this VRV a new life has began !!!

    We should always go back to basics that's a fact...

    Now i try to find a service manual for VRV III HR, i don' t want to start a new thread about it, i think an hope someone will link me to this document...

    rgds

    cool#9

  14. #14
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: E4 fault on RXYQ12P7

    Cool,

    Your wish is my command.

    Have a look at my website HERE and you will find what you wish for.

    (NO, not that long legged blond bird with a great pair you dream of but almost as good, ie the Daikin manual)

    PS. If you can't find it then look below the fault code downloads.

  15. #15
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: E4 fault on RXYQ12P7

    Quote Originally Posted by The Viking View Post
    Cool,

    Your wish is my command.

    Have a look at my website HERE and you will find what you wish for.

    (NO, not that long legged blond bird with a great pair you dream of but almost as good, ie the Daikin manual)

    PS. If you can't find it then look below the fault code downloads.
    Thanks The Viking but i need the same for Heat Recovery series.!
    The reason why is that in France it's quite difficult to get information.
    15 years ago i met a japanese technical manager who said to me " ***** everything you need to know about Daikin 's product is written in the SERVICE MANUAL...just take time to read it"
    Since i try to make my own collection of data and learn on the field.
    rgds
    cool#9

  16. #16
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: E4 fault on RXYQ12P7

    Sorry, my mistake
    (I just gave you the one for the model no you posted!)

    I will have another look and see if I got it lying around somewhere


    EDIT:
    Sorry but according to Daikin's website it hasn't been launched yet, so we probably have to wait a while for the manuals
    Last edited by The Viking; 23-10-2007 at 11:49 PM.

  17. #17
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: E4 fault on RXYQ12P7

    Quote Originally Posted by The Viking View Post
    Sorry, my mistake
    (I just gave you the one for the model no you posted!)

    I will have another look and see if I got it lying around somewhere


    EDIT:
    Sorry but according to Daikin's website it hasn't been launched yet, so we probably have to wait a while for the manuals
    Thanks again but i've found it after 1 hour on google... it's called Si 37-701 an now i can go ahead.
    rgds
    cool#9

  18. #18
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: E4 fault on RXYQ12P7

    Link to it?

  19. #19
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: E4 fault on RXYQ12P7

    Quote Originally Posted by The Viking View Post
    Link to it?
    See my PM please
    cool#9

  20. #20
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: E4 fault on RXYQ12P7

    http://207.45.127.154/daikin/Default.aspx?tabid=142
    Posted this link it already in another section
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Fault with Tango cassette
    By airefresco in forum Air Conditioning
    Replies: 8
    Last Post: 19-09-2007, 08:42 AM
  2. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM
  3. lg fridge/freezer fault light on function display board
    By bazza in forum Trouble Shooting
    Replies: 0
    Last Post: 25-02-2007, 03:25 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •