23-10-2007, 02:30 PM #1
cpc case controller
CPC CONTROLS
I have a cpc case controller which is bringing up a sensor short for all temp probes. When I reset the control, the sensors read the correct temps again and case controller works fine.
Is this due to a faulty temp probe or is the case controller playing up?
any ideas?
-
28-03-2008, 06:09 PM #2
Re: cpc case controller
Try this
Whilst the controller is working ok put a shorting wire across 1 of the probes at the controller (dont remove any probes) and see if this brings up the same fault (all probes faulty). If yes then you have 1 probe that is playing up. If no then you have to look at replacing the controller. As you say you can reset it after the test. I have had many a probe short out before and they are usually badly fitted and burnt through on a defrost heater or snagged somewhere.
I know its a harsh method but it should let you know what you need to.
Hope it helps
-
03-04-2008, 05:45 PM #3
Re: cpc case controller
Sounds like a faulty controller to me.
It could also be a network 'blip'
ChillinIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
09-04-2008, 01:58 AM #4
Re: cpc case controller
What type of CPC controller are you working with? Reflex? Einstein?
-
09-04-2008, 09:35 AM #5
Re: cpc case controller
I know this is an old thread but CPC make "transient resistors" to fit to their CCB's between the CCB and the probe connections, they are their to discharge any induced voltages to earth. What happens is a voltage builds up due to incorrect earthing, static electricity (most typical cause) or badly routed wiring and causes all inputs to show "short" or go crazy and read stupid temps. Mostly we find these affected cases to have the CCB's mounted under the case on or just above a vinyl floor, store RH is usually very low when these issues rear their heads as it is a static electricity build up causing the problem. We had a few sites that were a major issue and ended up getting CPC USA to come over and inspect and test - this was their finding.
...and she said "give it to me you big fridgie"
Similar Threads
-
Electronic controller probes wired wrong
By Electrocoolman in forum Trouble ShootingReplies: 3Last Post: 12-11-2007, 06:39 PM -
Daikin Hard wired controller
By marc5180 in forum Air ConditioningReplies: 16Last Post: 10-11-2007, 06:43 PM -
Help with new electronic refrigerator controller !
By EngiGal in forum New TechnologiesReplies: 17Last Post: 08-04-2006, 07:39 PM -
Controller wiring
By Mickvee in forum Air ConditioningReplies: 2Last Post: 30-12-2005, 02:04 AM -
Fan Controller
By Abe in forum Trouble ShootingReplies: 4Last Post: 12-01-2002, 02:21 AM