    cpc case controller



    CPC CONTROLS

    I have a cpc case controller which is bringing up a sensor short for all temp probes. When I reset the control, the sensors read the correct temps again and case controller works fine.
    Is this due to a faulty temp probe or is the case controller playing up?
    any ideas?



  2. #2
    Join Date
    Mar 2008
    Location
    United Kingdom
    Posts
    51
    Rep Power
    17

    Re: cpc case controller

    Try this
    Whilst the controller is working ok put a shorting wire across 1 of the probes at the controller (dont remove any probes) and see if this brings up the same fault (all probes faulty). If yes then you have 1 probe that is playing up. If no then you have to look at replacing the controller. As you say you can reset it after the test. I have had many a probe short out before and they are usually badly fitted and burnt through on a defrost heater or snagged somewhere.
    I know its a harsh method but it should let you know what you need to.

    Hope it helps

  3. #3
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: cpc case controller

    Sounds like a faulty controller to me.
    It could also be a network 'blip'

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  4. #4
    TreverXJ's Avatar
    TreverXJ Guest

    Re: cpc case controller

    What type of CPC controller are you working with? Reflex? Einstein?

  5. #5
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: cpc case controller

    I know this is an old thread but CPC make "transient resistors" to fit to their CCB's between the CCB and the probe connections, they are their to discharge any induced voltages to earth. What happens is a voltage builds up due to incorrect earthing, static electricity (most typical cause) or badly routed wiring and causes all inputs to show "short" or go crazy and read stupid temps. Mostly we find these affected cases to have the CCB's mounted under the case on or just above a vinyl floor, store RH is usually very low when these issues rear their heads as it is a static electricity build up causing the problem. We had a few sites that were a major issue and ended up getting CPC USA to come over and inspect and test - this was their finding.
    ...and she said "give it to me you big fridgie"

Similar Threads

  1. Electronic controller probes wired wrong
    By Electrocoolman in forum Trouble Shooting
    Replies: 3
    Last Post: 12-11-2007, 06:39 PM
  2. Daikin Hard wired controller
    By marc5180 in forum Air Conditioning
    Replies: 16
    Last Post: 10-11-2007, 06:43 PM
  3. Help with new electronic refrigerator controller !
    By EngiGal in forum New Technologies
    Replies: 17
    Last Post: 08-04-2006, 07:39 PM
  4. Controller wiring
    By Mickvee in forum Air Conditioning
    Replies: 2
    Last Post: 30-12-2005, 02:04 AM
  5. Fan Controller
    By Abe in forum Trouble Shooting
    Replies: 4
    Last Post: 12-01-2002, 02:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •