    basic refrigerator properties



    Hello, I am trying to get a basic feel for the power, COP, and cost of traditional refrigerators so that I can compare them to peltier devices. I know that refrigerators are typically much cheaper on large scales, but I am not sure exactly what happens on small scales. I have looked at some refrigerator spec sheets, but so far, they have not said anything about power or heat transfer. They only mention size and temperature. Can someone direct me to a good resource?

    Thank you,
    Andy



  2. #2
    Join Date
    Dec 2002
    Location
    Malaysia
    Age
    59
    Posts
    86
    Rep Power
    22
    Dear Andy,

    I can't help you with refrigerator specifics because as you correctly put it, they don't reveal much. But the compressor power and refrigerating capacity in W is most of the time given.

    Done a comparison some time ago between using thermoelectrics and mechanical refrigeration. Economically, due to high cost of TE modules , the traditional mech. ref. system is less than 1/3 the cost of using TE air-to-air modules. Do you have a cheap source of TE modules ?

    Bernard


  3. #3
    Join Date
    May 2002
    Location
    TN
    Posts
    124
    Rep Power
    22
    COP is watts of electricity divided by btus of heat removed. Spec sheets have BTUs and Watts on them. COP is easy to find.
    That is just the compressor though. The heat loss on the box detirmines how much compresser capacity you need. There are refrigerators out there the run on 1/3 the electricity of a standard refrigerator. Add a couple of inches of insulation to your frig and you will be able to see this too. Low power semi conductors can do a good job of cooling with lots of insulation.

  4. #4
    astein@lear.com's Avatar
    astein@lear.com Guest
    Thanks for your replies.

    To bersaga: Nope, no cheap source of Peltiers. Sorry. We're just investigating.

    To superheat: I have seen the BTUs mentioned with air conditioners, but not refrigerators. So far, I've just been going to GE's, Kenmore's etc. website and snooping around and their spec sheets haven't mentioned BTUs. If you get a chance, can you tell me where you've seen it?

  5. #5
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Actually, COP is a dimensionless number. Cooling capacity in Btu/hr divided by electrical input in watts gives you an EER value. One can convert EER to COP with the following:

    COP = EER / 3.412

    BTW, a SEER rating applies only to residential air conditioning equipment, and it involves several tests. So one cannot derive a SEER value simply knowing EER at some given operating condition.
    Prof Sporlan

  6. #6
    Join Date
    May 2002
    Location
    TN
    Posts
    124
    Rep Power
    22
    BTUs will be given on the compressor spec sheet. ASk the manufacturer.

    You are right Prof. I got those 2 backwards again. I have always wondered if the EER numbers on the compressor sheet really mean anything. Change the coils to a bigger or smaller size and the system has a new eff. with the same compressor. What is the standard they go by?

  7. #7
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    I have always wondered if the EER numbers on the compressor sheet really mean anything. Change the coils to a bigger or smaller size and the system has a new eff.
    Absolutely! EER values for a compressor are useful to know, but it is more important to get your coil and refrigerant line sizing correct if you're optimizing system efficiency.
    Prof Sporlan

  8. #8
    Join Date
    Dec 2001
    Location
    Cincinnati, Ohio, USA
    Age
    63
    Posts
    258
    Rep Power
    23
    Without having to get a 37 year college degree in heat transfer/fluid flow, how would you determine line size versus evaporator?

    What if you split a system?

  9. #9
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    I would size the line per the compressor's capacity at design conditions. I would not pay much attention to the evaporator.

Similar Threads

  1. What is the Basic Function of a Rapid Purger ?
    By eng_ab in forum Industrial
    Replies: 3
    Last Post: 11-06-2006, 07:53 PM
  2. Basic SMALL refigeration system
    By M@@Home in forum Fundamentals
    Replies: 13
    Last Post: 01-06-2006, 08:19 PM
  3. Help with a basic design for a Safari Vehicle
    By Jeromy Dacey in forum Domestic
    Replies: 0
    Last Post: 14-12-2005, 11:38 AM
  4. The Basic Law of MRC ?
    By MANIS in forum Air Conditioning
    Replies: 0
    Last Post: 23-09-2003, 09:21 PM
  5. basic operating principles of compressors
    By alanmongey in forum Fundamentals
    Replies: 2
    Last Post: 13-09-2001, 01:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •