Panasonic Inverter CU-S10JKP error kode H11. Help me..any body
Some one can help me.? what is meaning error code H11 and how fixed the problem ?
Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body
Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body
H11 Indoor / Outdoor abnormal communication
> 1 min after starting
operation
Indoor fan operation
only
• Internal / external cable connections
• Indoor / Outdoor PCB
Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body
Troubleshooting
When abnormality indication starts again
Is there any wiring error?
• Correct the indoor-outdoor units
connection wires
Check the indoor-outdoor units’ connection wires.
Disconnect terminal 3 wire and measure Vdc between terminal
2 & 3 from the outdoor unit.
Is the Vdc fluctuate between 20-70Vdc?
• Replace outdoor PCB
Reconnect terminal 3 wire and measure Vdc between terminal
2 & 3 from the outdoor unit.
Is the Vdc fluctuate between 20-50Vdc?
• Replace indoor unit PCB.
Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body
emailed ya the manual- 7meg
Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body
Quote:
Originally Posted by
fdharmala
hello any body ?
Steady on there fella.....giving just 4 MINUTES before you start shouting for help is a little impatient :eek:
We don't sit on here just waiting for questions you know :D
Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body
took me 12 minutes to reply- and e mail manual,must be getting old:rolleyes:
also its been over an hour and no thanks,email reply - cant ask for rep points off a new member:D
Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body
Quote:
Originally Posted by
install monkey
Troubleshooting
When abnormality indication starts again
Is there any wiring error?
• Correct the indoor-outdoor units
connection wires
Check the indoor-outdoor units’ connection wires.
Disconnect terminal 3 wire and measure Vdc between terminal
2 & 3 from the outdoor unit.
Is the Vdc fluctuate between 20-70Vdc?
• Replace outdoor PCB
Reconnect terminal 3 wire and measure Vdc between terminal
2 & 3 from the outdoor unit.
Is the Vdc fluctuate between 20-50Vdc?
• Replace indoor unit PCB.
Ok thankyou very much for help me. i'll chek the PCB and if i have any problem i'll give news soon.