Re: Building a wine cabinet
I made a wine cooler for my boss one time. All I did was replace the LT comp with HT compressor and change the valve to match. I also mounted the CU on 1" of soft rubber. I let the condensate drain into the box with an overflow at about 1". It served as a vacuum break as well.
If you wanted to display the wine, you could use a floral box. They tend to be cheaper than wine boxes.
The floral box is designed at about a 7degF T.D. in order to maintain high humidity levels (>90% R.H.). Wine should be kept at an R.H. of about 55% to 65%, primarily to keep mold from forming on the corks, and not damage the labels (moisture / condensation).
Accordingly, Wine room systems are designed at a 12degF to 15degF T.D., and preferably at long runtimes of 18 to 20 hours/day (for de-humidification).
In the case of short-term storage (merchandiser) however, I guess the conditions would not be that much of a concern.
... That is my experience.... (FWIW)
Cheers!