Daikin AHU
Hi can any one help on this one
Daikin AHU sorry can’t remember the model number but the display has A B C on it, no fault codes on the display no warning lights on, metered out the thermister check ok, transmitting to and fro from AHU and cond’s but will not bring on the out side unit, set at 18c, air on 28c, turn the power on it run’s on down to its set point then will not cut back on, indoor pcb change still the same, customers not very happy and my service manager
Help please
Ps condensate pump not wired into the control circuit
-
1 Attachment(s)
Re: Daikin AHU
Hi Jan,
Sorry doesn't ring any bells atached is he only list i have
Try ringing Space air on 01483 504883.
They have always been very helpful and spot time each time i have rang with a problem
Regards
Raymond
-
Re: Daikin AHU
We really do need to know the model type. Is the "emergency" switch in the correct position on the outdoor pcb? factory set is in the "white" area. Any changes to switches must be followed by a power reset.
If you ring Space Air the first thing they will ask for is a model and serial number.
-
Re: Daikin AHU
Thanks for the replies, have been in contact with tech support did all the checks they suggested still no joy, model number on my paper work in my van will have to come back on that one thanks
-
Re: Daikin AHU
Hi jan.
Daikin is not sold in my country but, in all cases when an AHU started going funny, I've found a wire disconnected in the controls part.
Have a check for a loos wire, who knows, it might be your day. :cool:
Chemi
-
Re: Daikin AHU
up date, went back with more info, AHU working perfect ?