Re: Verco display freezer
Hi Iceman,
Verco's do suffer from high rates of pobe failures and yes as soon as the evap probe plays up the defrost go all over the place. HRP do the probes 255807 rings a bell for some reason the ends come loose on the old ones. Piece of cake to replace you should do both in about 10mins
Regards
Raymond
Re: Verco display freezer
Thanks for the info Raymond. Will pop into HRP Monday and pick up the part. Amazingly, this fault has been going on for a few years, and the last company couldn't sort it out.
Best Wishes
James
Re: Verco display freezer
If it’s still the original carel stat I would change the lot .just changing the probe you might get called back because of the controller.
Re: Verco display freezer
Just had another thought although not probably related.
If the controller starts to play up check the transformer if it is a 12v one. You should allow 10% either way but the transformers have a habbit of going up o 15v and causing controller faults. HRP also have a large stock of these too and i tend, if changing the controller to do the transformer at the same time
Regards
Raymond
Re: Verco display freezer
Thanks to both of you for the info. Probably won't get the authorisation from the customer's head office for about 72 hours anyway. I don't suppose you would know what the fault code is E0 changing to E1 and back again every few seconds.
Regards
James
Re: Verco display freezer
i think EO is air probe fault and E1 is Evap probe fault