150 ton trane screw chiller
Hey guys,
I have a 150 ton trane screw chiller that has been going off on some oil faults. There are a bunch of ports on the compressors to connect gauges to, however none are labeled and trane is of no help. They will not give up the information, they send me some bull $hit manual tnat tells you nothing. Does anyone have experience with this machine? Its a. Rtac 150
Thankyou in advance
Mike
Re: 150 ton trane screw chiller
what are these fault codes?
the chiller should discribe what kind of fault this is?
low oil flow?loss of oil?
once you tell us what the nature of these faults are you will get more responses!
if you mail me i will send you the relevant manual..
good luck
Hi guys,
Can u explain exact diagnostic it is high oil temp or low oil flow.so we will defenetly help to you also send your email id will send the manual.
http://www.mediafire.com/view/?ai8zwflpc99wilz
page 70 shows port connections on compressor- also shows how to check the oil level too
i am lookind for trane spare parts do you know where i get.
trane.....
tarunenrser58
The original post by miked123 was posted in regards to the machine I am working on.
The machine is a Trane Rtac-155 with remote evaporator. In the diagnostic history the unit had a code of 198 "low oil flow". However, after starting the machine up, I have yet to have that error duplicate. I have had error codes 6b3 "low evap temp" and error
Code 8a "evaporator water flow ( high approach temperature )" these codes shut the unit down on three attempts to start. On the fourth attempt the machine came online and continued to run without trouble. I am wondering why at initial start-up this issue was present.
Hi Johnny
The plot thickens!
Maybe you had some initial cavitation or gas pockets which have now cleared?
Who knows!
All well that ends well eh!
A high fives to install monkey for that manual. That was a huge help in regards to oil level assessment. Thanx for that!! Grizzly - the machine is a runn'in... We will see what today brings....!
Turned out the unload solenoid on compressor 2A was not functioning properly due to the coil of solenoid was not fully seated on shaft of solenoid. Chiller is up and runn'in...
