Daikin vrv control wiring
(a) Approx 8 outdoor units.
(b) Approx 98 indoor units.
Would it be possible to daisy chain all indoor units e.g starting from top floor all the way down to the bottom floor and also link the outdoor units?
There will be no central control used on the project. All units will be individually controlled.
I have a feeling that I will have to daisy chain the vrv's individually, which will be unfortunate!
regards
Jase
Re: Daikin vrv control wiring
Jase each systems indoor fan coils F1 & F2 wiring have to be kept seperate. Even when not using a Centralised controller i would still recommend connecting the F1 & F2 outdoor connections on your eight outdoors this will enable the sequential start. If you need any more help just let us know the model numbers of your units:)
Re: Daikin vrv control wiring
Cheers for the advice puddleboy!:)
Re: Daikin vrv control wiring
Hello puddleboy3
send to me type:PC9316
Thanks & Regards
Re: Daikin vrv control wiring
Hi Jase,
There is impossible to daisy chain all indoor units, should be system by system seperately as puddleboy said.
If not over capacities error, spec are 130% or 200% option for cooling only unit and 150% for heatpump.
Daikin never locked and prompted as capactiy error unlike others.
However please seperate.