Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
reefermechanic
Hi reeferC
welcome on board:))
Have you try work the normal operation to the reefer? You have to set the set temperatureto -18.0 C and pls note when return temperature to the -18.0 C. I no know have you check to the inside of reefer container. If there is damage on buffer plate and evaporator fan blades reefer unit doesn't cool. Check them pls.
good luck
reefer mechanic
First, thanks so much for very quickly reply,
Yes, i set unit -18C for cooling, as i said ''it run until about -10C to -12C, automatically actived deforst by system'', can't reach to -18C (i don't know why, i think this made pretrip's lasted). Return & Supply are normally, they different 6C. Also i've check evap motor fan, blade are OK, only the humidity sensor is cut, Inside, plate's good. Seem problem is why it run until about -10C to -12C, automatically actived deforst ?
Hope u know.
Thanks again,
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
ReeferC
First, thanks so much for very quickly reply,
Yes, i set unit -18C for cooling, as i said ''it run until about -10C to -12C, automatically actived deforst by system'', can't reach to -18C (i don't know why, i think this made pretrip's lasted). Return & Supply are normally, they different 6C. Also i've check evap motor fan, blade are OK, only the humidity sensor is cut, Inside, plate's good. Seem problem is why it run until about -10C to -12C, automatically actived deforst ?
Hope u know.
Thanks again,
Hi ReeferC
I think air comes from outside to inside container.
Pls check all them below mationed then reply to me.
* Check the condenser coil. Dirty or clean?
* Check the isolation of evaporator fan motor acces panels. There must be isolation for air bypass. You know this? Black insulating tape to the top of back of acces panels.
* Check the door rubber of container doors.
* Chek the Compressor service valves or liquid line shutoff valve
partially closed?
* check insulation of air vent door. Also it must be fully close.
good luck
see you
reefer mechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi there reefer C, have you checked the TX valve. I had one not to long ago that would do the same. We narrowed it down to the TX Valve. It will go into defrost if it detects there is no difference in supply and return
e.g evaporator coil iced up. Try taking it off auto defrost and running it you will see what the suction pressure is doing. The TX valve might be closing prematurely, this can be caused by moisture in the system, have yiou tried a new filter drier and refrigerant charge
Try these and see where you go
good luck
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi, Thanks so much 4 replying reefer mechanic, phil Landon.
I've checked this unit in this morning, problem i think that's WATER inside, have amount of water inside reefer container, maybe water pipe's choed up & 4 drains hose can't open. So the time to pretrip is long. Tommorow, my coworker will clean inside then try to PTI it again, then i'll report to u.
@ phil Landon, i'll pay attention to ur ideas. Thanks
Thanks again 4 reply,
Goodluck all.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi all, some days im so busy, I checked, problem is Water inside. After cleaning, do PTI again & Passed.
Thanks 4 all rp.
Bdgs
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Mr. Reefer mechanic help me can u give me a manual and part list of daikin decosIIIb i can't find the supply sensor of that unit ;( tnx this is my email address lilgenesis_19@yahoo.com and kh31lan@gmail.com
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi, i am having a problem with a thermo king rd II 50 tci dual temp unit have chaecked and had charged with ***** but still cannot get the unit to cool everything seems to be working but it acts like there is a vavle or something some where not letting the ***** cool the unit neither unit will cool front or rear and also if any one has a manual on this unit i would really appreciate it as i cannot get the fan on the rear evap unit to run it has no power to the fan motor any hepl would be greatly appreciated my email is sid_sidney2002@yahoo
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
also this is a 1995 model unit
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Tsk tsk i have a problem my unit have a heavly frosting in suction side of compressor the model of my unit is 69nt40-501 i dont know what is the problem when the unit is -5 its starting to have frosted help me :(
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
is the unit modulating? some older units do frost up quite a bit on the compressor can u run the unit to 0 & -20 and can u tell me the pressures at these temps
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
kheilan
Mr. Reefer mechanic help me can u give me a manual and part list of daikin decosIIIb i can't find the supply sensor of that unit ;( tnx this is my email address
lilgenesis_19@yahoo.com and
kh31lan@gmail.com
hi khelian
pls you should say unit's model number.
see you.
reefer mechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
sid_sidney
hi, i am having a problem with a thermo king rd II 50 tci dual temp unit have chaecked and had charged with ***** but still cannot get the unit to cool everything seems to be working but it acts like there is a vavle or something some where not letting the ***** cool the unit neither unit will cool front or rear and also if any one has a manual on this unit i would really appreciate it as i cannot get the fan on the rear evap unit to run it has no power to the fan motor any hepl would be greatly appreciated my email is sid_sidney2002@yahoo
hi,
is that reefer container unit??
see you
reefer mechanic.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
kheilan
Tsk tsk i have a problem my unit have a heavly frosting in suction side of compressor the model of my unit is 69nt40-501 i dont know what is the problem when the unit is -5 its starting to have frosted help me :(
hi khelian,
you can check pls txv valve and defrost sensor.
good luck
reefer mechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
ReeferC
Hi, Thanks so much 4 replying reefer mechanic, phil Landon.
I've checked this unit in this morning, problem i think that's WATER inside, have amount of water inside reefer container, maybe water pipe's choed up & 4 drains hose can't open. So the time to pretrip is long. Tommorow, my coworker will clean inside then try to PTI it again, then i'll report to u.
@ phil Landon, i'll pay attention to ur ideas. Thanks
Thanks again 4 reply,
Goodluck all.
Hi reeferC,
best information when clogged drain hose.thnks.
see you
reefer mechanic.
thanks
emmmm aa few months agoaa too
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
it was a truck mounted 24 foot box that i have put on a trailer that we are going to use for cold storage as it is diesel with the electric stand by
Quote:
Originally Posted by
reefermechanic
hi,
is that reefer container unit??
see you
reefer mechanic.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
now have the unit cooling had a leaking compressor seal and a bad throttling valve but still really need a manual for this as i still cant get the evap fan for the other unit to come so i really need the wiring diagrams for this so i can trace it back to find my problem
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi,Im new need to know how to daignose thermoking relay board>mp3000
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
i have this daikin reefer shutdown alarm E107,E101
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
have u check the codes ,maybe its on e auto fresh
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
Tifare Jone
i have this daikin reefer shutdown alarm E107,E101
Hi Tifare Jone
Welcome on board:))
you have to check EEV ( electronic expansion valve) , dryer and refrigerant level in the system. Also you have to check condenser coil. Condenser coil must be clean when high ambiant temperatures.
good luck
see you
reefer mechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Need a spare parts manual for the above. Can any one direct me to a link where I can download a PDF file.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Good day Reefer mechanic,
Have a problem with DAIKIN reefer LXE10E-1....showing alarm F803(abnormilities) unit stop.........after restaring the unit cleared the alarm unit till working fine. Dnot know for how long it will work fine. Please need help from you to troubleshoot.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Rohit, this alarm top2 alarm type for daikin units. Have you got recovery machine? You have to recovery all refrigrant from system. Then you to have to make deep vacuum. It must be about one hour. Then you can charge the refrigerant again to the system. But right level. Check pls refrigerant level for your unit on the label left of compressor. If there is air or moisture in the system unit shows F803 alarm code. I m waiting your reply problem solved or not solved. Good luck. Reefer mechanic.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Refermechanic,
I find that you have little knowledge of HVAC systems. I am very concerned that I need to communicate a new product designed with a Daikin air conditioning system, but this I do not have the Daikin Communication Protocol were, or at least the algorithm to calculate the frame check sequence.
Could you help me with something, please, it is very important to me.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
xorteleco
Hi Refermechanic,
I find that you have little knowledge of HVAC systems. I am very concerned that I need to communicate a new product designed with a Daikin air conditioning system, but this I do not have the Daikin Communication Protocol were, or at least the algorithm to calculate the frame check sequence.
Could you help me with something, please, it is very important to me.
Hi xorteleco
i would like to help you. What do you need?
see you
reefermechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic,
I'm trying to figure out what the frame check code using Daikin in communications between the thermostat and the indoor unit through air conditioning systems.
Do you know anything about this protocol or where I can find information about it?
Thank you very much!
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hello everyone, I need your help i have to change software thermo king MP 3000 but when i try that one message in my log man (check the compatibility between controler and log men) now i want jast restar the reefer in the furst situation but the conntainer in mode flush load ,icut power and restar also reefer in mode flush load,,the rrefer is full ans set pont -35c.plz help
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
reefermechanic
Hi xorteleco
i would like to help you. What do you need?
see you
reefermechanic
Hi reefermechanic,
I'm trying to figure out what the frame check code using Daikin in communications between the thermostat and the indoor unit through air conditioning systems.
Do you know anything about this protocol or where I can find information about it?
Thank you very much
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi all,
i am indra from Indonesia.
in this 2weeks i'am looking for the following compressor in Indonesia and Singapore. but still can not find the compressor. maybe someone here can help me to figure out this compressor.
MISUBISHI Compressor Type : RS 2514ESH1 No ALA 201 AD 19 type ***** R22. Use for Freezer container.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi everyone,
is anyone aware where can i have a thermoguard upVI rebuild any place in europe??? i am aware of erickson, rte but they are located in the states. anybody in europe???
appreciate your help,
nikolas
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Try the Carrier Transicold Electronics REbuild Center in Rotterdam details at http://www.performanceparts.carrier....csbrochure.pdf
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello there!!!can i ask what is LEAK BACK to the compressor and PUMPING OIL???im so curious o.O
"Be a very good listener and someday you will become a very good speaker"
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Reefer709
You probably have a contaminated system because of impure refrigerant. You will need to flush out the system with dry nitrogen and than do a deep vacuum with a vacuum pump. Recharge fresh refrigerant and try running the unit.
Rgds
Sukhdev
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi Guys
I am very new to RE. Ai am facing a peculiar problem with a new Carrier Primeline unit done just 1 voyage. During AUTO PTI 2 i get failure in P6-5. Although i have replaced the compressor i still get this failure in AUTO PTI2. Can any one suggest remeady. I am sure there is some external fault in this unit.
Tks/Rgds
Sukhdev
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Sorry guys but can you tell me how to put in a new thread. I am confused.
Tks
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
terminal
hello everyone, I need your help i have to change software thermo king MP 3000 but when i try that one message in my log man (check the compatibility between controler and log men) now i want jast restar the reefer in the furst situation but the conntainer in mode flush load ,icut power and restar also reefer in mode flush load,,the rrefer is full ans set pont -35c.plz help
Hi Terminal,
You need a laptop ( has got RS232 port) and and software program of TK ( smartsponge) . Have you got these?
see you
reefer mechanic
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Quote:
Originally Posted by
sukhdevsuri
Hi Guys
I am very new to RE. Ai am facing a peculiar problem with a new Carrier Primeline unit done just 1 voyage. During AUTO PTI 2 i get failure in P6-5. Although i have replaced the compressor i still get this failure in AUTO PTI2. Can any one suggest remeady. I am sure there is some external fault in this unit.
Tks/Rgds
Sukhdev
Hi Sukhdev,
Pls say the model number of your reefer unit ? 69NT40XX
see you
reefermechanic.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi all bros,
Is there anyway to disable (not display on screen) DAL86, AL67 (Carrier) by keypad (without using laptop or replacing materials) for case of emergency ?
Thanks so much.
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
transicold carrier training courses....
Icon Legend
School Registration Closed / Full
School Location Changed
School Dates Changed
School Cancelled
To view a course description, or register for a school - click on the course date in the table
below.
For further information about training on refrigerated containers, please contact Jack Kurz at
+1.315.432.7608 or David Whyte at +1.315.432.6411.
Course Dates Registration Deadline Course Title Location No. Student Enrollment
08/29/2012 -- 08/30/2012 30.07.2012 2-Day Controlled Atmosphere Valparaiso, Chile 2249 26 of 24 students
09/03/2012 - School CANCELLED 03.08.2012 1-Week Container - SPANISH ONLY San Jose, Costa Rica 2252 12 of 24 students
09/11/2012 -- 09/13/2012 10.08.2012 Advanced 3-Day Container Product Update Puerto Madryn, Argentina 2238 13 of 12 students
09/12/2012 -- 09/13/2012 13.08.2012 Advanced 2-Day Container Product Update Surubaya, Indonesia 2232 20 of 20 students
09/18/2012 -- 09/19/2012 06.08.2012 Advanced 2-Day Container Product Update Cape Town, South Africa 2231 14 of 24 students
09/24/2012 -- 09/28/2012 20.08.2012 1-Week Container - SPANISH ONLY Guayaquil, Ecuador 2253 24 of 24 students
09/24/2012 -- 09/25/2012 22.08.2012 2-Day Gen Set Montreal, Canada 2254 4 of 24 students
09/24/2012 -- 09/26/2012 24.08.2012 Part A - 3 Day Refrigerated Container Basic Tauranga, New Zealand 2233A 26 of 24 students
09/25/2012 -- 09/26/2012 24.08.2012 Advanced 2-Day Container Product Update Mombasa, Kenya 2241 8 of 12 students
09/26/2012 -- 09/28/2012 24.08.2012 3-Day Container Product Update - ENGLISH ONLY Montreal, Canada 2255 8 of 24 students
09/27/2012 -- 09/28/2012 27.08.2012 Part B - 2 Day Refrigerated Container Advanced Tauranga, New Zealand 2233B 24 of 24 students
10/09/2012 -- 10/10/2012 31.08.2012 Advanced 2-Day Container Product Update Izmir, Turkey 2234 3 of 12 students
10/22/2012 -- 10/26/2012 21.09.2012 1-Week Container Xiamen, China 2235 22 of 24 students
11/05/2012 -- 11/06/2012 08.10.2012 2-Day Gen Set Long Beach, CA 2256 1 of 24 students
11/07/2012 -- 11/09/2012 12.10.2012 3-Day Container Product Update Long Beach, CA 2257 1 of 24 students
11/14/2012 -- 11/15/2012 15.10.2012 Advanced 2-Day Container Product Update Yokohama, Japan 2236 0 of 12
-
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Kheilan
Leak back is the amount of refrigerant that will pass backwards through the compressor when it is stopped. All units even brand new have some leak back and is the reason that the Suction and discharge pressures equalise while the compressor is stopped. Pumping oil is exactly what it says all compressors have an internal oil pump which operates from the crankshaft or motor shaft direct drive to circulate, pump oil through the bearings.