Fiddling with the settings will not solve the problem. There are quite a number of settings that need to be applied to each system at commissioning based on the output of the selection software, to optimise the ssystem to your particular location, situation and home. Changing 1 or more individually can have a negative effect. The Altherma is a specialist bit of kit and needs careful design, good installation and setting up by a fully trained technician, to get the best out of it.
You don't say what type of Altherma you have, Monobloc, Low Temp, High Temp, Bivalent, Series 1,2, 3 etc. but whichever you have, they all need the same specialist attention.
I,ve seen good installs and a lot that leave you asking yourself if the installers should be allowed to even purchase the kit, where trained monkeys could have done better. The poor old customer is always left disappointed and out of pocket in cases such as this.
One installation I was asked to investigate came about where the customer (in the middle of Lincolnshire) had spent considerable money on building a new house with underfloor heating throughout and heated by 2 Althermas to give sufficient heat load. Problem was, when the ambient temp dropped to -11C at night, the house would not come up above 14C! Turned out that the underfloor heating had been designed to give 21C with an ambient of 3C - typical CIBSE design criteria. He wasn't too pleased when he asked me how he could get it working correctly, to which I said 'you need to rip up the underfloor heating coils and re-install them with additional loops to increase output'
Have a look at page 234 onwards of the Altherma 3 manual which shows the Field Settings - 10 pages of it.
https://www.daikin.co.uk/content/dam...de_English.pdf
You can then appreciate that just changing the 'Offset' will not cure your problem. What you need is for Daikin themselves to attend and review your installation - it will be money well spent in my opinion and at least you will then know what, if anything, you will need to do to get your system operating correctly, and at what cost.