Re: Evaporator Distributors
Had one do the same thing, think was Friga-bohn but don't quote me on that. Basically the distributor was two 3/16ish sized cap tubes poked into a 1/2" thing with a flare nut to suit the tev. One 3/16 was at 12 o'clock and the other at 6 o'clock as the distributor was horizontal.
Gravity made all the liquid go through the lower one and had same symptoms you describe, out with the spanners, turn distributor so outlets were at 3 and 9 o'clock and it worked fine.
Re: Evaporator Distributors
Thanks for the reply monkey spanners, But the TEV is mounted vertically feeding in to the distributor in this instance so I believe that it can be eliminated. But you are correct in what you are saying, as nozzle type distributors are required to be mounted vertical to work properly. This distributor is a venturi type as mention in post and can supposedly be mounted in any direction.
Any how an update on the days preceding. Manufacturers engineer came out to have a look at wat was going on. I was asked to put a larger orifice in the TEV so I did, the existing orifice was the correct size. The result to my eyes was exactly the same except the TEV was hunting even more. The suction line to the compressor quickly turned to a block of ice. But according to their so called engineer this was just cold vapour. What tish I know the difference between cold vapour and liquid lucky it has an accumulator. Anyway was room was still wasn't pulling temp so I was asked to open up the TEV superheat even more. At this point I stopped and ask the engineer are they going to warrant the compressor when the valve plate is annihilated from slugging liquid. No. Well I'm not opening it any more. So we agreed to disagree. The manufacturer says there is nothing wrong even though there clearly is.
So after discussion it was decide bite the bullet and that we replace the evaporator with a new one from another manufacturer at our cost. As if we left it the way it was it was only going to cause another 5 service calls under warranty. As a reputable company we can't have this, so tomorrow it is getting replaced I let you know how I go!
Re: Evaporator Distributors
Fridgey. Can you send a picture or two of the distributor and feed to your evap?
Re: Evaporator Distributors
is the tev correctly fitted, sized correctly and for the correct application- sensing bulb lower than the tev head, bulb insulated? correctly mounted on the suction line at 9 o clock?
Re: Evaporator Distributors
New evaporator coil went in today, similar capacity to the evaporator being pulled out. I used the same TEV but went back to the original sized orifice and reset to factory setting. Of course pipes, electrical's and mountings are never the same, but after some rejigging the new evap was in and connected. After a vac out all was ready to go, and what do you know it ran like a dream. It pulled the room down from 20C to -18C in under two hours, the TEV superheat across the coil was 7K and was steady and not hunting, suction superheat was 14K, a massive difference to the previous coil.
What I know is that I would never use another evaporator from the original manufacturer again. Although I won't name names, previously I thought they had a good product but since manufacturing has been moved out of Australia obviously the product quality has slipped. Their lack of acknowledgment of even a problem to me is shear arrogance, but the proof is in pudding as the new coil works perfectly!