Re: Velocity at air terminal
5.56 cubic metres per second and face velocity at intake at 11.33 Ln metres per second, will not work. Fan will cavitate and be extremely noisy. Larger discharge duct and bigger intake grille required
Re: Velocity at air terminal
Hi Magoo,
Thanks for your advise.
The fan is at the end in the fan house, which got the louver @ 1050x1000.
The wire mesh (700x700) with 3 nos. So I believe that will not be 11.337 m/sec.
Thanks for your time
Re: Velocity at air terminal
Now you mention a design difference.
Re: Velocity at air terminal
Sorry Magoo for my poor language skills and presentation.
Re: Velocity at air terminal
Get the fan suppliers fan curve graph chart, establish the total fan static with a pitot tube or differential gauge and read off the chart. Then establish actual volume flow. Google engineering toolbox for all formulas and calculations