Re: expansion valve sizing
first you have to learn how TEV is works,
2nd you need these information ,discharge & suction pressure - Room temperature-Evaporator temperature - Evaporator Capacity - and ....
3rd in table you chose your TEY.
Re: expansion valve sizing
First you need to choose the right size evaporator for your job, above or below zero, kind of defrost if any, Humidity required in the cold room, etc. etc.
Choosing the TXV depends of evaporating temp, refrigerant to be used.
Last comes condensing unit to fit the chosen capacity and ambient temp.
Re: expansion valve sizing
Pls go through sporlan , danfoss , alco ,catalogs ......... Selection procedures are well explained therein
Re: expansion valve sizing
Try this Sporlan Literature site, it has just about everything that you need to know.
http://www.sporlanonline.com/literature.shtml
Re: expansion valve sizing
thanks for your reply, i think i need some time to check it..